So it's contractual, not philosophical.   Presumably, the installing
contractor tests it ... 

I don't think we're talking about testing the backflow appliances itself
for functionality - that's best left for the "certified backflow
technician."   If you pump up an UG including the BFP, the relief valve
will only operate when there's a differential between the clappers.  So
an RPZ or RPDA usually weeps a bit when you pump it up, but once the
line is equalized you can run a conventional hydro.  And if you just
want to test against it, you can pump up through the FDC or main drain
or the supply-side tap on the riser check, if so equipped.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Thursday, May 29, 2008 7:10 PM
To: Steve Leyton
Subject: Re[2]: 200 psi test for components rated 175

Hello Steve,

I start 1' AFF with my work. I sub out any underground installation work
I get (which I try to avoid) and it is up to them to test it. Only
question I have is how do you get an RPZ to hold the back pressure to
hydro to it? Pump the system up through the #1 test cock?

-- 
Best regards,
Charles Thurston 
 Coastal                            mailto:[EMAIL PROTECTED]

Thursday, May 29, 2008, 6:55:37 PM, you wrote:

> I'll bite - why not?   If the Fire Department pumps into the FDC,
isn't
> it likely to back pressure the BFP to at least 150?  And if so,
wouldn't
> it be prudent to test the assembly?

> Steve Leyton
> Protection Design & Consulting


> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Charles
> Thurston
> Sent: Thursday, May 29, 2008 3:30 PM
> To: IPA
> Subject: Re: 200 psi test for components rated 175

> Hello IPA,

> I for one have never put 200 on the backflow, I will not either.

> Thursday, May 29, 2008, 6:03:25 PM, you wrote:

>> I've got this question posed to me:

>> Backflow preventor is rated at 175 (as are most of the fire sprinkler
>> components) yet we are required to do a 200 psi test. Is the keyword
> here
>> "working pressure" of 175 psi or am I missing something?

>> thx,
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to