Hello Steve,

I start 1' AFF with my work. I sub out any underground installation work I get 
(which I try to avoid) and it is up to them to test it. Only question I have is 
how do you get an RPZ to hold the back pressure to hydro to it? Pump the system 
up through the #1 test cock?

-- 
Best regards,
Charles Thurston 
 Coastal                            mailto:[EMAIL PROTECTED]

Thursday, May 29, 2008, 6:55:37 PM, you wrote:

> I'll bite - why not?   If the Fire Department pumps into the FDC, isn't
> it likely to back pressure the BFP to at least 150?  And if so, wouldn't
> it be prudent to test the assembly?

> Steve Leyton
> Protection Design & Consulting


> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Charles
> Thurston
> Sent: Thursday, May 29, 2008 3:30 PM
> To: IPA
> Subject: Re: 200 psi test for components rated 175

> Hello IPA,

> I for one have never put 200 on the backflow, I will not either.

> Thursday, May 29, 2008, 6:03:25 PM, you wrote:

>> I've got this question posed to me:

>> Backflow preventor is rated at 175 (as are most of the fire sprinkler
>> components) yet we are required to do a 200 psi test. Is the keyword
> here
>> "working pressure" of 175 psi or am I missing something?

>> thx,
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to