What actually qualifies someone to calibrate a gauge? Is the
calibrator certified? Is it someone that knows how to do it? Is it
someone that does it regularly? Is it someone that works for a company
that sells lots of instruments? Is it someone other than you? I've got
a device to do this that I use in class to demonstrate relationships
and measurements. Am I qualified or not? I've watched the guy at the
instrument company certify gauges for me and his regular job is
working the will call counter. Now that doesn't mean he doesn't have
some special qualification beyond knowing how to be able to put that
tag on the gauge but I don't know. And if you need to be certified who
regulates it and what's the standard of care? Seems to me that any one
of us could calibrate our own gauges.

On Fri, Aug 1, 2008 at 8:59 AM, Thom McMahon <[EMAIL PROTECTED]> wrote:
> RE-testing a fire pump for not using calibrated gauges, is an AHJ issue.
> Calibration is only required once a year as far as I can see, for any
> testing device. By doing that it doesn't mean that your gauges are correct
> or in spec.(it means they were when they were tested.) Just as with BFP you
> can test and pass a device, and then disconnect and re-connect your gauge,
> and it will fail. Was the first test wrong or a failure? NO. At the time of
> the test it passed. Does that indicate or mean anything about any other
> time? NO. Calibration for Fire protection is more Just A "Warm Fuzzy" than
> an indication of the exacting science of our profession. As you said on a
> fire pump test your matching a pre-determined curve, any large variation
> would alert you to an issue such as a bad gauge.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple
> (forum)
> Sent: Thursday, July 31, 2008 8:20 PM
> To: [email protected]
> Subject: RE: Gauge Calibration
>
> Tom,
>
> Fortunately it was a small pump and the gauge in question was the one used
> on the single hose monster. Fortunate our pump rep. had one in his van with
> the calibration paperwork.
>
> Why would I need to re-test when the calibration is not required by NFPA 20
> (03)?
>
> Ken
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
> Sent: Thursday, July 31, 2008 6:12 PM
> To: [email protected]
> Subject: RE: Water Supply
>
> Ken if you're doing BFP testing you get your test sets calibrated each year,
> you can send your gauges in at the same time. Personally we keep two sets
> and that way we are never without one as they expire one month apart.
>  Additionally if you run into this problem at test, I would offer to run the
> test, then insert the gauge in an envelope addressed to the calibration co,
> record the serial # of the gauge. (If it doesn't have one write one on it in
> marker. Note that # on the test report. Offer to let the AHJ stick it in the
> mail, and include a request that the AHJ be copied on the Calibration
> report. When it comes back, if it's within 1% your test is complete, if not
> you may have to re-test, which it sounds like you have to do anyway.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple
> (forum)
> Sent: Thursday, July 31, 2008 2:41 PM
> To: [email protected]
> Subject: RE: Water Supply
>
> Ok guys and gals.....here's one for ya.
>
> Just did a pump acceptance test under 2003 edition of NFPA 20. The inspector
> shows up on site and asks for calibrated gauges. Even though we pulled out a
> gauge that came from the factory 3 months ago, he wanted to see the
> paperwork. (I guess he didn't like the dirt that was on the gauge either
> from a previous diesel pump flow test. Turns out things get muddy when you
> do those) After reviewing NFPA 20 (03) I see that there is not a requirement
> for gauge calibration except in the appendix, to which no tolerance for the
> gauges is given.
>
> I questioned the inspector on the requirement and asked for a code
> reference. What I got back was the re-write that appears in the 2007 edition
> of the acceptance procedure that does note that gauges must be calibrated
> and within +/- 1%. I'm fine with that, except for the fact that here in
> Pennsyltucky and in his jurisdiction, the 2003 is the applicable standard.
>
> Now to take it one step further, the new NFPA 20 (07) mentions that the
> gauges must be calibrated annually (depending on use...kinda open ended
> don't ya think?). In speaking with some folks that supplied our shiny 4 1/2"
> Glycerine filled gauges, they mentioned that we could get them calibrated,
> but "what are you gonna do, get them calibrated after every use?" They do
> mention in the literature for our gauges (that I sent to the AHJ) that they
> are calibrated at the factory. Keeping in mind that scientists are probably
> using their "top of the line" gauges to measure the force of an atom
> bouncing of a cow's butt.
>
> I mentioned to the AHJ that in the meantime (till the 2007 ed comes around),
> the township could purchase a calibrated gauge and use that as a benchmark
> and throw the contractor's gauge(s) on a static point of the system if they
> think something was tampered with.
>
> I would be curious to see how others would handle this. AHJs especially.
> You'ins keep my life interesting.
>
> Getting calibrated gauge paperwork isn't a big deal (well it is if they
> spring this on you at the time of test), but trying to enforce rules that
> haven't been adopted yet kinda crosses the line in my book.
>
> By the way, I did check out NFPA 291 (forgot the edition), there was mention
> of calibration, but no mention of tolerance.
>
> I have a headache from bouncing my head off the soapbox.
>
> Ken Holsopple
> Design Manager & Gauge Calibration Coordinator
> Rowe Sprinkler Systems
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.138 / Virus Database: 270.5.10/1584 - Release Date: 7/31/2008
> 12:00 PM
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.138 / Virus Database: 270.5.10/1585 - Release Date: 8/1/2008
> 6:39 AM
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to