Depends on your calendar. Julian? Gregorian? imperial Chinese?
Sumerian? Remember Ken, the October Revolution happened in November.

On Fri, Aug 1, 2008 at 10:45 AM, Ken Holsopple (forum) <[EMAIL PROTECTED]> 
wrote:
> The last couple posts (Mr Greenman, Thom and Mr. Fletcher) have hit on what
> is driving me nuts about the whole thing. The code enforcement person, along
> with the fire inspector, seem to view the calibration paperwork as some kind
> of guarantee. Try explaining that one without a marker board......
> It makes me wonder about the accuracy of the atomic clock. For all I
> know....today is tomorrow or yesterday.
>
> In speaking with the gauge rep this morning I also found out that they can
> do a multiple point test relatively cheep, but can also match it with NIST
> standards (whatever they may be), but that involves tearing the gauge apart
> and it sounds expensive.
>
> I got a little more info this morning and it seems the inspector had a
> situation on his hands where a contractor used a rigged gauge(s). In my
> response I noted (again) that the only way to solve this for the AHJ to
> bring his/her own gauge and check with the contractors gauge in a static
> condition. I noted that calibration will not solve underhandedness. (Is that
> a word? Spell check seems to think so) Also mentioned to him to have the
> contractor drop the gauge to 0 at the end of a hydrostatic to eliminate the
> possibility of the scotch tape trolls messing with the gauge.
>
> The fire inspector had just been to a seminar on fire pumps where
> calibration was part of the subject matter. I AM glad he went to the fire
> pump seminar (NFPA 20 07 edition I am guessing), but cautioned him to use
> filters because it doesn't change the applicable edition he is to enforce. I
> know the AFSA folks have been pretty clear on all there phone seminars.
>
> And YES I have learned quite a bit about calibration and gauges.
>
> Ready to go back to sticking my thumb in the hose stream and guessing.
>
> As for digital (tee-hee) I still get a kick out of seeing calcs with res
> pressure that runs out to 3 decimal points. :) Round up?
>
> Ken
> Flow Test Scientist - I ordered a nifty lab coat for pump tests.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to