This is the section I was waiting to hear someone identify. I personally say you don't need to open 6 hydrants to get a 25% drop provided you meet or exceed the system demand.

A 31 gpm difference is insignificant but unless you hit the magical 25%, you have to go with the demands of the AHJ. Suggesting an outside source for education is warranted. Any bets that such a suggestion would be well received?

Roland

On Jul 31, 2008, at 12:38 PM, John Drucker wrote:

Eric,

Good point. In order to be accurate sufficient water must be flowed to
attain a 25% drop in pressure. (NFPA 291-4.3.6)

As a plan reviewer I've seen plenty of flat tests and back they go.
Wheres that stick.

John Drucker

-