To update everyone that helped. We had a meeting with the AHJ and after
talking he understood I was below the curve and he accepted the 31 GPM. He
originally misunderstood and thought I was above my curve. Had to do some
tweaking of the system to bring my safety factor up but it was approved.
Thanks to all of you that helped, it is much appreciated. I'll buy you all a
frosty mug of glycerine. Hey I have to get rid of the stuff somehow. Lol

Joe Burtell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, August 04, 2008 10:32 AM
To: [email protected]
Subject: Re: Water Supply

This is the section I was waiting to hear someone identify.  I  
personally say you don't need to open 6 hydrants to get a 25% drop  
provided you meet or exceed the system demand.

A 31 gpm difference is insignificant but unless you hit the magical  
25%, you have to go with the demands of the AHJ.  Suggesting an  
outside source for education is warranted.  Any bets that such a  
suggestion would be well received?

Roland

On Jul 31, 2008, at 12:38 PM, John Drucker wrote:

> Eric,
>
> Good point. In order to be accurate sufficient water must be flowed to
> attain a 25% drop in pressure. (NFPA 291-4.3.6)
>
> As a plan reviewer I've seen plenty of flat tests and back they go.
> Wheres that stick.
>
> John Drucker
>
> -
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to