I'm looking forward to the day when all the gauges are digital and we
won't have to guess if the pitot pressure from the 4" hydrant butt is
28.4 or 28.8 (lmao). It could be critical if your local sprinkler
scientist won't let you slide on 31 gpm.

Happy Friday everyone,

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, August 01, 2008 8:59 AM
To: [email protected]
Subject: RE: Gauge Calibration

RE-testing a fire pump for not using calibrated gauges, is an AHJ issue.
Calibration is only required once a year as far as I can see, for any
testing device. By doing that it doesn't mean that your gauges are
correct
or in spec.(it means they were when they were tested.) Just as with BFP
you
can test and pass a device, and then disconnect and re-connect your
gauge,
and it will fail. Was the first test wrong or a failure? NO. At the time
of
the test it passed. Does that indicate or mean anything about any other
time? NO. Calibration for Fire protection is more Just A "Warm Fuzzy"
than
an indication of the exacting science of our profession. As you said on
a
fire pump test your matching a pre-determined curve, any large variation
would alert you to an issue such as a bad gauge.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
(forum)
Sent: Thursday, July 31, 2008 8:20 PM
To: [email protected]
Subject: RE: Gauge Calibration

Tom,

Fortunately it was a small pump and the gauge in question was the one
used
on the single hose monster. Fortunate our pump rep. had one in his van
with
the calibration paperwork.

Why would I need to re-test when the calibration is not required by NFPA
20
(03)?

Ken

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Thursday, July 31, 2008 6:12 PM
To: [email protected]
Subject: RE: Water Supply

Ken if you're doing BFP testing you get your test sets calibrated each
year,
you can send your gauges in at the same time. Personally we keep two
sets
and that way we are never without one as they expire one month apart.
 Additionally if you run into this problem at test, I would offer to run
the
test, then insert the gauge in an envelope addressed to the calibration
co,
record the serial # of the gauge. (If it doesn't have one write one on
it in
marker. Note that # on the test report. Offer to let the AHJ stick it in
the
mail, and include a request that the AHJ be copied on the Calibration
report. When it comes back, if it's within 1% your test is complete, if
not
you may have to re-test, which it sounds like you have to do anyway.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
(forum)
Sent: Thursday, July 31, 2008 2:41 PM
To: [email protected]
Subject: RE: Water Supply

Ok guys and gals.....here's one for ya.

Just did a pump acceptance test under 2003 edition of NFPA 20. The
inspector
shows up on site and asks for calibrated gauges. Even though we pulled
out a
gauge that came from the factory 3 months ago, he wanted to see the
paperwork. (I guess he didn't like the dirt that was on the gauge either
from a previous diesel pump flow test. Turns out things get muddy when
you
do those) After reviewing NFPA 20 (03) I see that there is not a
requirement
for gauge calibration except in the appendix, to which no tolerance for
the
gauges is given. 

I questioned the inspector on the requirement and asked for a code
reference. What I got back was the re-write that appears in the 2007
edition
of the acceptance procedure that does note that gauges must be
calibrated
and within +/- 1%. I'm fine with that, except for the fact that here in
Pennsyltucky and in his jurisdiction, the 2003 is the applicable
standard.

Now to take it one step further, the new NFPA 20 (07) mentions that the
gauges must be calibrated annually (depending on use...kinda open ended
don't ya think?). In speaking with some folks that supplied our shiny 4
1/2"
Glycerine filled gauges, they mentioned that we could get them
calibrated,
but "what are you gonna do, get them calibrated after every use?" They
do
mention in the literature for our gauges (that I sent to the AHJ) that
they
are calibrated at the factory. Keeping in mind that scientists are
probably
using their "top of the line" gauges to measure the force of an atom
bouncing of a cow's butt.

I mentioned to the AHJ that in the meantime (till the 2007 ed comes
around),
the township could purchase a calibrated gauge and use that as a
benchmark
and throw the contractor's gauge(s) on a static point of the system if
they
think something was tampered with.

I would be curious to see how others would handle this. AHJs especially.
You'ins keep my life interesting.

Getting calibrated gauge paperwork isn't a big deal (well it is if they
spring this on you at the time of test), but trying to enforce rules
that
haven't been adopted yet kinda crosses the line in my book.

By the way, I did check out NFPA 291 (forgot the edition), there was
mention
of calibration, but no mention of tolerance.

I have a headache from bouncing my head off the soapbox.

Ken Holsopple
Design Manager & Gauge Calibration Coordinator 
Rowe Sprinkler Systems 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.5.10/1584 - Release Date:
7/31/2008
12:00 PM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.5.10/1585 - Release Date:
8/1/2008
6:39 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to