Chuck,

As a code official I'm merely citing the code. Does that mean I agree,
in many cases no.

However according to the bazillion posts, conversations and outright
complaints I've read, designers and contractors want code officials to
follow the code, agree ?

With that said as a designer, its your prerogative to provide protection
above and beyond the code, we merely review for technical compliance.
But make sure you advise the property owner because invariably they call
us asking if its required by code and we have no choice but to cite the
code.

That's the way it is. I'm a firefighter too and given my druthers
everything and I mean everything would be suppressed.

John Drucker
  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of RFI -
Bismarck
Sent: Monday, August 25, 2008 10:37 AM
To: [email protected]
Subject: RE: Re[2]: Elevator Pits and approved plans

In regards to the elevator protect / not to protect...  As a sprinkler
system "designer" and a fellow firefighter... I have some pictures of an
elevator fire from a University campus building here in the area that
evac'd the building... starting on top of the elevator... and caused
massive $$ dollar damage.  NO SPRINKLERS... 

Contact me off-forum and I can forward you the pics that I have...

RFP Chuck

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Sunday, August 24, 2008 7:40 AM
To: [EMAIL PROTECTED]
Subject: Re[2]: Elevator Pits and approved plans

Hello Cherokeefirepro,

When the elevator installers complain about my heads in the shaft and
tell me they are not needed I make them supply me and the AHJ proof they
are not needed. Most times I get to eliminate the head from the top of
the shaft, The head at the bottom is for the trash that is known to
buildup down there.

Saturday, August 23, 2008, 5:51:04 PM, you wrote:

> One more question has anyone supplied documentation of hydraulic fluid
being non-combustible?
> This came up in the forum last year and I recall someone using FM data

> to
show that a
> high flash point would meet the intent of NFPA 13.  
> ------Original Message------
> From: Forest Wilson
> Sender: [EMAIL PROTECTED]
> To: [email protected]
> ReplyTo: [email protected]
> Subject: Elevator Pits and approved plans
> Sent: Aug 23, 2008 5:07 PM

> We are doing work in Westerville, Ohio. A school is installing a 
> "Limited
Use/ Limited
> Application" elevator. We submitted plans indicating approporiate
modifications to the
> existing sprinkler system to accomodate the new elevator shaft and
mechanical room.
> Our plans showed no sprinkler coverage in the elevator shaft. It 
> showed a
sprinkler in
> the elevator mech room with a water-flow switch to act as a
shunt-trip.
The plans were stamped and approved.
> We completed the job and during the final inspection, the local 
> building
inspector and
> fire inspector questioned why there is no sprinkler in the shaft and
demanded that we
> supply documentation to the city regarding this. They also questioned 
> why
we installed a
> nwaterflow switch for the sprinkler in the mechanical room. When I
explained that it was
> to act as a shunt-trip and showed them my copy of the NFPA 13 
> handbook,
they replied
> that they've never seen that before and we would have to supply
documentation on that as well.
> Of course, they are not Plan Examiners. They are Inspectors there to
ensure compliance
> with the Approved Plans. They refused to sign off on our installation.

> Has anyone encountered this before? Did you fight them through a 
> formal
appeals process or just do whatever they wanted?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


> Sent from my Verizon Wireless BlackBerry


--
Best regards,
Charles Thurston
Coastal Fire Protection
 Coastal                            mailto:[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 270.6.7/1632 - Release Date:
8/25/2008
7:05 AM
 

No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 270.6.7/1632 - Release Date:
8/25/2008
7:05 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to