Have you ever seen C900 (Blue Brute) so named for a reason with a 3/4" thick
wall. I see the solvent attack as the tough one, if it's not in a warehouse
with lots of Mario fork lift drivers. Slope floor away from riser to the
required drain? (All rooms containing a backflow preventer are required to
have a drain and a relief drain.)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Monday, August 25, 2008 2:21 PM
To: [email protected]
Subject: Re: 13, 2007 23.1.6.1.2

Would it be possible to sleeve the plastic from say 18" or so below
grade to the flange? Seems like mechanical protection is the issue.

On Mon, Aug 25, 2008 at 1:11 PM, Ed Kramer <[EMAIL PROTECTED]> wrote:
> Interestingly, at least one company (Uni-Flange) makes an adapter flange
for
> C900 pipe (http://www.uniflange.com/ucats/ufa900.pdf).
> Appropriate listings may be a problem, but I know it's been used on fire
> lines.
>
> Ed Kramer
> Littleton, CO
>
>
>
>
>> Then the rise from the base elbow must always be metallic pipe. How
>> would
>> you go from PVC to steel above the floor if you don't have a flange or a
>> groove to work with?
>>
>> Art/ATCO
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.6.7/1632 - Release Date: 8/25/2008
7:05 AM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to