Cause there is nothing in the code that I am aware of that gives a rating
with ordinary sprinklers at any spacing.  The 6' comes in about openings in
floors and as an alternate in the atriums.  These are two specific
situations addressed but not a general 1 hr rating.  The floor opening has
nothing to do with ratings and the atrium needed a solution to rating before
the development of the Tyco heads once code officials decided to allow
multiple floors to be connected without a traditional rating.  

Tyco heads are listed and tested to the same standard as other rated
construction methods for ratings.  It's the same test for sheetrock and
concrete.  If you have a corridor that requires a rating Tyco heads are the
only code complying solution I am aware of if using sprinklers. 

And to Craig's comment if it's unrated then you don't need any sprinklers on
the glass.  

Of course standard note and discussion point regarding a contractor choosing
methods of rating vs. the architect and engineer who should have specified
methods.    

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Tuesday, September 30, 2008 7:21 AM
To: AFSA
Subject: Window Sprinklers

Mornin'. I am bidding a project which consists of an educational facility.
Down the center of the building runs an 8' wide corridor. 60' of one of the
corridor walls is glass. The corridor walls are fire rated so I am
installing sprinklers on both sides of the glass at a max. of  6' spacing.
Tyco makes a sprinkler expressly for this use. I can find nothing in codes
or standards that require me to use this Tyco sprinkler. Does anyone know of
a requirement to use this sprinkler? Why would a contractor choose to use an
$80.00 Tyco sprinkler when a $3.00 SSP will do the same job? This makes me
concerned that there is one sorta like the CC1 and CC2 sprinkler.

Any input will be greatly appreciated.



 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to