A HA!!!   That's the point, isn't it?  That the architect failed to
completely design the building and account for the protection of windows
and likely, the limitations of the window sprinklers in terms of
mullions, doors, etc., etc.   And the fact that they just waved the
magic sprinkler wand at the condition with a note means that they've
deferred the PROBLEM, but not necessarily the solution.

Along this thread, it was asked where, in NFPA  13, this is addressed
and it isn't.   The Tyco WS is a patented, specific application
sprinkler that, when installed in accordance with its relatively lengthy
and articulate listing criteria, can be used to achieve protection of up
to 2 hours on rated glass.   Where it says that is in its listing and in
what's known as the ICC Evaluation Service, or ICC-ES.   I believe it's
public domain and that you can surf the site whether or not you're an
ICC member, but if you track down ICC-ES report #NER-516, you'll find
that it puts the product into context of how it should be applied per
the building code.   

As a consultant, I try to program the use of window sprinklers as early
as possible in the process.   They can be thirsty hydraulically,
especially if you have a lot of them in the design area like a
conference room or showroom application where there's more than one side
of the compartment in the design area.  They have very particular
spacing requirements and they are best designed in close coordination
with the architect because usually there will be some means of
concealing the sprinklers for aesthetic purposes, as with a valance.
And you have to account for window coverings and the type of joints,
mullions, etc., etc.    And it's the ARCHITECT'S responsibility to
foresee all of this, which they usually don't.

I would strongly recommend downloading both the ICC-ES report and the
Tyco PDS from their web site and carefully reviewing all the conditions
of installation before you bid and ultimately take ownership of this
design.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, September 30, 2008 6:55 AM
To: [email protected]
Subject: RE: Window Sprinklers

It's permitted this way so what's a fellow to do? Tell the
Architect/Engineer, Building Department, Fire Department and owner that
they have to eliminate the doors and horizontal mullions from 80 ft. of
glass wall? And by the way, the next time you want to use a glass wall
you have to check with Tyco?

By the time we find out about the rated glass wall all the permits are
issued and construction has begun. It's probably a little too late to
architecturally redesign the entire lobby area.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Scott A.
Futrell
Sent: Tuesday, September 30, 2008 6:16 AM
To: [email protected]
Subject: RE: Window Sprinklers

The Tyco limitations are because that is what is required to keep the
glass intact, make the sprinkler work properly, and ensure the wall
rating.  If it is designed, installed, approved, and accepted
incorrectly it is still wrong regardless of what the AHJ approves. With
all due respect Ron, you won't be okay if something goes wrong and you
haven't used the Tyco sprinkler given that it is available for this
specific application and the information in the thread below including
Chris' input.

Scott   

(763) 425-1001 Office 
(612) 759-5556 Cell 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, September 30, 2008 7:59 AM
To: [email protected]
Subject: RE: Window Sprinklers

If the AHJ will approve closely spaced sprinklers you should be okay.
The Tyco window sprinkler has some severe limitations like no horizontal
mullions which translates to no doors.

Just because a sprinkler is UL Listed for an application it doesn't mean
it's the only thing that can be used. We at the office have often
discussed submitting a line of sprinklers to UL for testing and sending
along a tanker truck of water from phoenix for the test. We would then
have the only sprinkler UL Listed with Phoenix water. Following the
window sprinkler logic everyone would have to buy our sprinkler if they
did work in Phoenix. (lol)

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Tuesday, September 30, 2008 5:21 AM
To: AFSA
Subject: Window Sprinklers

Mornin'. I am bidding a project which consists of an educational
facility.
Down the center of the building runs an 8' wide corridor. 60' of one of
the
corridor walls is glass. The corridor walls are fire rated so I am
installing sprinklers on both sides of the glass at a max. of  6'
spacing.
Tyco makes a sprinkler expressly for this use. I can find nothing in
codes
or standards that require me to use this Tyco sprinkler. Does anyone
know of
a requirement to use this sprinkler? Why would a contractor choose to
use an
$80.00 Tyco sprinkler when a $3.00 SSP will do the same job? This makes
me
concerned that there is one sorta like the CC1 and CC2 sprinkler.

Any input will be greatly appreciated.



 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3482 (20080930) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to