Well if you want to be innovative then by all means be so.  On projects such as 
this if the contractor has a better idea, I'm all for it and then we will sit 
down and see how it will integrate into the overall picture.  But if there was 
no direction given on projects like this where there's 20lbs stuffed in the 
10lb bag, guess who will be the loser every time, you guessed it boys and 
girls, the sprinkler contractor.

So if you get innovative and there's extremely limited space and you venture 
off on your own, get ready to install it and reinstall it more than once, at 
your expense.  Did you coordinate like the specs directed you?

The problem with a lot of AE firms is even IF they do have competent design/3D 
modeling persons, they can't coordinate with something that isn't there.  If 
it's not in the model, it doesn't exist is pretty much the normal viewpoint.  
So if you're not part of that effort, you're on your own.  Hope you bid high 
enough.

Fire protection is always treated as the "red-head step child" in the 
engineering world.  To most people fire protection is a waste of money, it 
makes no profit, is expensive and takes up valuable space, then it becomes a 
life-long maintenance headache.  So any time we can get it recognized as being 
a vital discipline and building system and included in any level of detail in 
the overall project design, I'll take it.

We're just trying to put a better product on the streets than the typical big 
"X" on the drawing whenever possible to make the more complex projects flow 
better.  Hopefully at the end of it all everybody goes home with a few more 
bucks in their pocket and a positive experience, instead of saying "OH $%^&* I 
wish we had never taken that job!"

Oh and I know that ALL disciplines have been engineering in 3D since the 
beginning of time.

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, November 11, 2008 1:14 PM
To: [email protected]
Subject: RE: White papers and definition of roles

Right on George. With all the special systems I would expect more than $2k 
difference in the specialty equipment quotes and the prices should be closer if 
you take away the opportunity for innovation of design by the bidders.

Our prices are higher on jobs requiring 3D or BIM. We find there is very little 
coordination and more "here is where we are so now you
(sprinkler) can go around us. It's like a 3D retrofit. The only thing that 
changes is we spend more design time to come up with the same product. Besides 
we FP contractors have been doing 3D since the beginning of time, it's just 
that the presentation has been 2D.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Tuesday, November 11, 2008 7:00 AM
To: [email protected]
Subject: RE: White papers and definition of roles

Ummm, maybe the two bidders had breakfast together on bid morning?
Don't throw your elbow out patting yourself on the back.

Coincidence or a comp price is far more likely to produce bids within .001% of 
each other than quality of the bid documents.

Seriously, if you'd given em a stocklist, a finished, coordinated dwg, and a 
rational schedule, there'd be more difference in the price than this just on 
how different companies allocate OH, backlog needs, lift pricing renting vrs 
owning, mileage from office to site variance, mix of each contractor's design 
talent pool $ cost, workman's comp experience reflected in what could be 
drastically different rates, skill of the two estimators, whether someone got 
something last night- There are so many variables, I'd suspect a comp number 
before a headless piping layout as the root cause for the close resemblance.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Tuesday, November 11, 2008 8:46 AM
To: [email protected]
Subject: RE: White papers and definition of roles

Speaking of bid prices.  We performed our first AutoCAD based 3D integration of 
fire protection on a recent project.  Our typical corporate deliverable is the 
design criteria and a floor plan with equipment on it.  (I have had a couple 
complete installation level design requests but they are rare in this
industry)  Typical criteria based design, no piping, or heads or anything else. 
 (because the contractor will do it for free).  Anyway,  as we've progressed 
into the 3D realm I've pushed to get fire protection included in the 3D 
modeling.  Convincing the powers that be that by at least including mains and 
branch lines into the model and coordinating their locations and elevations 
will aid the contractor during installation, reduce his design time and reduce 
change orders and bring us tighter bids as there is less for the imagination 
and more solid information to work with.

So they let us do the piping layout but no heads, so we did the layout in the 
model dealing with equipment, steel and other modeled obstructions.


Two weeks ago the project went out for bids.  We had 3 bidders.  One dropped 
out due to various personal reasons but the bids came back yesterday from the 
other two.

The fire protection bids on the project were within $2,000 of each other.
Now that may not sound like a big deal but understand the total above ground 
fire protection is valued at almost $1.5 million dollars.

For two bidders to be that close is pretty unusual.  But it validated the need 
for better design other than the old floor plan with the note "follow NFPA 13" 
and similar stuff.

Hopefully we can continue this trend within our company.  I know this would be 
difficult for many companies because there is a lack of qualified people who 
can actually layout a fire protection system and this project ran the gamut of 
system types from wet, dry, pre-action, foam-water deluge, low expansion foam, 
dry chemical, CO2 and a proprietary, IR triggered, high
speed, deluge curtain system (that is really cool by the way).

Now I'm hoping that our management sees the value in this effort and will 
continue down this path.  Convincing some to allow us to provide more than the 
bare minimum of fire protection information is a tough fight.  For whatever 
reason is has been for years.  Maybe it has to do with the lack of qualified 
people, some of it is based on economics, some of it is perceived value, like I 
said, most AE firms feel the contractor provides the engineering effort for 
free so why do anything other than a spec and some fancy notes.

I actually had one PM complain that the sprinkler contractors ALWAYS put their 
pipe in the wrong place and it has to be torn down and removed.
He
caught me on a good day so I graciously (stop snickering)  reminded him of the 
directive we typically give sprinkler contractors:  1. coordinate with everyone 
and everything.  But at the same time all we give them is a floor plan of the 
building, no process piping layouts (because there is no such animal), no steel 
plans, no duct layouts, etc.  So how can he coordinate with things that don't 
exist or haven't been designed yet?  Hence my sales pitch for getting it in the 
model and then giving that info to the contractor.

But this is one I will put in the WIN column.  They come far and few between so 
forgive me while I savor the moment....................




Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Monday, November 10, 2008 6:16 PM
To: '[email protected]'
Subject: RE: White papers and definition of roles

Then there are those jurisdictions such as ND where you not only don't get 
registered in a specific discipline, but complaints will not be investigated 
unless there is a problem with the design. E.g., simply being trained in 
structural engineering and signing someone's sprinkler system design is not a 
problem that will be investigated.  It may violate the engineers' code of 
ethics, but it won't see action from the State Board unless there arises some 
issue with the design. So if you're a PE not trained in sprinkler design, just 
get some non-PE designer to complete the work and then you can seal it. 
Effectively there is no problem.  If the building burns as a result of improper 
design, then you've got a problem.

Of course, how many MEs even attempt to design a system?  It's pretty difficult 
to hold an engineer to the fire when his "design" boils down to "do it per 
code." I have had MEs ask me why I would ever attempt to provide a complete 
sprinkler system design.  They wonder, "doesn't that expose you to more 
liability?" Gee, and here I thought design and the associated liability was the 
whole point of our profession.

But that leads us right back to Thom's point about doing whatever is easiest.  
And when an ME gets paid on a percentage of construction, there's no sense 
putting time into a project and exposing himself to more liability.
Besides, his lack of effort will typically result in higher bid prices and 
therefore higher fees.  And the contractors don't want to rock the boat because 
the engineer may make their life more difficult. So the cycle continues.

I ought to write an article...

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079

[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to