One of the consistent problems we have up here is the electrician.
They don't take part in the coordination process, they often don't
even have CAD drawings and they just run everything where they want.
And the GC's tend to let them get away with a lot of it. I find that
more problems with the architect's concepts surface in the sprinkler
design that any of the other trades.
At 11:54 AM 11/12/2008, you wrote:
Well if you want to be innovative then by all means be so. On
projects such as this if the contractor has a better idea, I'm all
for it and then we will sit down and see how it will integrate into
the overall picture. But if there was no direction given on
projects like this where there's 20lbs stuffed in the 10lb bag,
guess who will be the loser every time, you guessed it boys and
girls, the sprinkler contractor.
So if you get innovative and there's extremely limited space and you
venture off on your own, get ready to install it and reinstall it
more than once, at your expense. Did you coordinate like the specs
directed you?
The problem with a lot of AE firms is even IF they do have competent
design/3D modeling persons, they can't coordinate with something
that isn't there. If it's not in the model, it doesn't exist is
pretty much the normal viewpoint. So if you're not part of that
effort, you're on your own. Hope you bid high enough.
Fire protection is always treated as the "red-head step child" in
the engineering world. To most people fire protection is a waste of
money, it makes no profit, is expensive and takes up valuable space,
then it becomes a life-long maintenance headache. So any time we
can get it recognized as being a vital discipline and building
system and included in any level of detail in the overall project
design, I'll take it.
We're just trying to put a better product on the streets than the
typical big "X" on the drawing whenever possible to make the more
complex projects flow better. Hopefully at the end of it all
everybody goes home with a few more bucks in their pocket and a
positive experience, instead of saying "OH $%^&* I wish we had never
taken that job!"
Oh and I know that ALL disciplines have been engineering in 3D since
the beginning of time.
Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, November 11, 2008 1:14 PM
To: [email protected]
Subject: RE: White papers and definition of roles
Right on George. With all the special systems I would expect more
than $2k difference in the specialty equipment quotes and the prices
should be closer if you take away the opportunity for innovation of
design by the bidders.
Our prices are higher on jobs requiring 3D or BIM. We find there is
very little coordination and more "here is where we are so now you
(sprinkler) can go around us. It's like a 3D retrofit. The only
thing that changes is we spend more design time to come up with the
same product. Besides we FP contractors have been doing 3D since the
beginning of time, it's just that the presentation has been 2D.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Tuesday, November 11, 2008 7:00 AM
To: [email protected]
Subject: RE: White papers and definition of roles
Ummm, maybe the two bidders had breakfast together on bid morning?
Don't throw your elbow out patting yourself on the back.
Coincidence or a comp price is far more likely to produce bids
within .001% of each other than quality of the bid documents.
Seriously, if you'd given em a stocklist, a finished, coordinated
dwg, and a rational schedule, there'd be more difference in the
price than this just on how different companies allocate OH, backlog
needs, lift pricing renting vrs owning, mileage from office to site
variance, mix of each contractor's design talent pool $ cost,
workman's comp experience reflected in what could be drastically
different rates, skill of the two estimators, whether someone got
something last night- There are so many variables, I'd suspect a
comp number before a headless piping layout as the root cause for
the close resemblance.
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, November 11, 2008 8:46 AM
To: [email protected]
Subject: RE: White papers and definition of roles
Speaking of bid prices. We performed our first AutoCAD based 3D
integration of fire protection on a recent project. Our typical
corporate deliverable is the design criteria and a floor plan with
equipment on it. (I have had a couple complete installation level
design requests but they are rare in this
industry) Typical criteria based design, no piping, or heads or
anything else. (because the contractor will do it for
free). Anyway, as we've progressed into the 3D realm I've pushed
to get fire protection included in the 3D modeling. Convincing the
powers that be that by at least including mains and branch lines
into the model and coordinating their locations and elevations will
aid the contractor during installation, reduce his design time and
reduce change orders and bring us tighter bids as there is less for
the imagination and more solid information to work with.
So they let us do the piping layout but no heads, so we did the
layout in the model dealing with equipment, steel and other modeled
obstructions.
Two weeks ago the project went out for bids. We had 3 bidders. One
dropped out due to various personal reasons but the bids came back
yesterday from the other two.
The fire protection bids on the project were within $2,000 of each other.
Now that may not sound like a big deal but understand the total
above ground fire protection is valued at almost $1.5 million dollars.
For two bidders to be that close is pretty unusual. But it
validated the need for better design other than the old floor plan
with the note "follow NFPA 13" and similar stuff.
Hopefully we can continue this trend within our company. I know
this would be difficult for many companies because there is a lack
of qualified people who can actually layout a fire protection system
and this project ran the gamut of system types from wet, dry,
pre-action, foam-water deluge, low expansion foam, dry chemical, CO2
and a proprietary, IR triggered, high
speed, deluge curtain system (that is really cool by the way).
Now I'm hoping that our management sees the value in this effort and
will continue down this path. Convincing some to allow us to
provide more than the bare minimum of fire protection information is
a tough fight. For whatever reason is has been for years. Maybe it
has to do with the lack of qualified people, some of it is based on
economics, some of it is perceived value, like I said, most AE firms
feel the contractor provides the engineering effort for free so why
do anything other than a spec and some fancy notes.
I actually had one PM complain that the sprinkler contractors ALWAYS
put their pipe in the wrong place and it has to be torn down and removed.
He
caught me on a good day so I graciously (stop snickering) reminded
him of the directive we typically give sprinkler contractors: 1.
coordinate with everyone and everything. But at the same time all
we give them is a floor plan of the building, no process piping
layouts (because there is no such animal), no steel plans, no duct
layouts, etc. So how can he coordinate with things that don't exist
or haven't been designed yet? Hence my sales pitch for getting it
in the model and then giving that info to the contractor.
But this is one I will put in the WIN column. They come far and few
between so forgive me while I savor the moment....................
Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Monday, November 10, 2008 6:16 PM
To: '[email protected]'
Subject: RE: White papers and definition of roles
Then there are those jurisdictions such as ND where you not only
don't get registered in a specific discipline, but complaints will
not be investigated unless there is a problem with the design. E.g.,
simply being trained in structural engineering and signing someone's
sprinkler system design is not a problem that will be
investigated. It may violate the engineers' code of ethics, but it
won't see action from the State Board unless there arises some issue
with the design. So if you're a PE not trained in sprinkler design,
just get some non-PE designer to complete the work and then you can
seal it. Effectively there is no problem. If the building burns as
a result of improper design, then you've got a problem.
Of course, how many MEs even attempt to design a system? It's
pretty difficult to hold an engineer to the fire when his "design"
boils down to "do it per code." I have had MEs ask me why I would
ever attempt to provide a complete sprinkler system design. They
wonder, "doesn't that expose you to more liability?" Gee, and here I
thought design and the associated liability was the whole point of
our profession.
But that leads us right back to Thom's point about doing whatever is
easiest. And when an ME gets paid on a percentage of construction,
there's no sense putting time into a project and exposing himself to
more liability.
Besides, his lack of effort will typically result in higher bid
prices and therefore higher fees. And the contractors don't want to
rock the boat because the engineer may make their life more
difficult. So the cycle continues.
I ought to write an article...
Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)