No one gets shot on this forum (I hope), all opinions are appreciated.

To play devils advocate though what would you do if the load height were
10 ft. instead of 5? The top of the first tier would be 15 ft. off the
floor.

I don't agree with the "source of ignition would probably be at the
floor level". I think the most likely source would be a hot load
containing something that ignites after sitting in the rack for a few
hours or days.

Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matsuda,
Richard
Sent: Monday, January 05, 2009 9:04 AM
To: [email protected]
Subject: RE: 1st Level of in-rack sprinklers location

110-feet?...woohoo...I don't think I've ever seen anything like this.
I'm glad I asked before I stuck my foot in my mouth.

I'll have to agree with Todd and change my answer to No, put the 1st
level of rack sprinklers at 10-foot as shown in the figure. 
The storage arrangement is an extreme...and any source of ignition would
probably be at the floor level. Having two levels of rack sprinklers
instead of one level below 20-feet seems like a better design to control
the fire in the incipient stages. This is just my opinion so don't shoot
me.
rick matsuda
city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher,
Ron
Sent: Monday, January 05, 2009 9:46 AM
To: [email protected]
Subject: RE: 1st Level of in-rack sprinklers location

1. 110 ft. storage.
2. Every other level as shown in 17.3.4.1.3(d).
3. Class IV and Group A in cartons.

In this case it makes one level of sprinklers difference and in this
building it's a lot of sprinklers.

Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matsuda,
Richard
Sent: Monday, January 05, 2009 7:52 AM
To: [email protected]
Subject: RE: 1st Level of in-rack sprinklers location

Ron,
My answer is maybe yes...but I'd like to know the full extent of the
storage before I agreed.
1. How high is the total storage? The chart is for over 25-feet high.
2. Where are the 2nd and 3rd levels of rack sprinkler located?
3. What is being stored? 
Not that any of these questions make a difference, but I'd like to know
what I'm agreeing to before it's all said and done.

Another question of similar nature...If your total storage arrangement
is 35-feet high, do you design for the total height of 35-feet or only
30-feet high since the lower 5-feet is dead space?

rick matsuda
city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher,
Ron
Sent: Monday, January 05, 2009 8:21 AM
To: [email protected]
Subject: 1st Level of in-rack sprinklers location

Anyone want to take a shot at this?

Figure 17.3.4.1.3(d) indicates the first level of sprinklers to be 10
ft. approximately from the floor and is shown above the second cube in
the elevation view.

If there is a 5 ft. dead space (empty with no storage or other
equipment) from the floor to the bottom of the first level of storage
could the first level of in-racks be above the second cube but
approximately 15 ft off the floor? It's in a rack supported bldg. with
automated pickers so the machine can't go low enough to use the first
four or five feet from the floor so the space is empty.

Hope you all have a happy new year.

Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)