In reality, the format used is whatever the architect or owner says it will be. 
When I got started in the consulting side of this biz in 2001 I started 
introducing the area design teams to the concept of sprinklers in Division 13.  
On a few occasions, the owner or the architect changed it back to Div. 15 
because they had never seen Div. 13 used for sprinklers and/or they didn't want 
to confuse the bidding contractors. Now many have changed to the 2004  (6 
digit) format; many are still using the older format; some still keep 
sprinklers in Div. 15.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, January 07, 2009 9:30 AM
To: [email protected]
Subject: RE: The Engineering Problem (RE: another fire - this will be 
interesting)

I think sprinklers are now known as 21.xx.xx (it's a six-place number
system).   We had it all figured out and then CSI went and TOTALLY
mucked it all up.   This, of course, is how they stay in business and
keep selling MasterFormat.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
McMahon
Sent: Tuesday, January 06, 2009 3:51 PM
To: [email protected]
Subject: RE: The Engineering Problem (RE: another fire - this will
beinteresting)

My final thoughts on this. (I Promise!)

When you see spec.'s in Div 15 for fire sprinkler it's a good indication
that they don't know fire sprinklers, or haven't updated their spec
since
1986 when Fire Sprinklers moved to Div. 13. (That's right you've been
seeing
the same "Canned" spec that is at least 23 years old. Possibly older
than
some on this forum.)
When you see a spec. in DIV. 13, but you local code is NFPA 13 2007,
know
that Fire Sprinklers were no longer in Div. 13 when 2007 was adopted,
and
may not include all its changes and provisions. (In 2004 Fire
Suppression
was moved to its own DIV. 21)(Alarms are in DIV 28)