Why would you include hose streams in #13R? Do you include 750 GPM hose on ESFR?
glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Thursday, January 08, 2009 7:07 AM To: [email protected] Subject: RE: Apartment Building I always include hose on that type of system (unless it is an impounded water supply with no connections) At 01:47 AM 1/8/2009, you wrote: >Watch out! I don't think you can delete hose allowance for the parkade, as >it is included in the design criteria for 13. Anyway, I have always included >it. Can someone else confirm? > >Tony > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Ken Holsopple >(forum) >Sent: January 7, 2009 11:12 AM >To: [email protected] >Subject: RE: Apartment Building > >"Can the garage be protected with a 13 System and the apartments on top be a >13R System?" > >David, > >Depending on the area height limitations allowed by your state building >code, the entire building could be done per 13R if the parking garage is for >use by the tenants of that building and not "open to the public". Keep in >mind that 13R gives guidance for areas outside the dwelling unit which would >be designed similar to a 13 system without things like a hose allowance. > >There was a discussion awhile back that might appear in the archives >pertaining to this very issue you may want to look up. > >Best Regards, >Ken Holsopple >Design Manager >Rowe Sprinkler Systems, Inc. > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Autry, David >Sent: Wednesday, January 07, 2009 10:30 AM >To: [email protected] >Subject: Apartment Building > >I think I know this but I want to verify. > >Two story apartment building on top of a parking garage. > >Can the garage be protected with a 13 System and the apartments on top be a >13R System? > >David Autry >Plans Examiner >Nebraska State Fire Marshal's Office >246 S. 14th Street >Lincoln, NE 68508 >402-471-9659 >402-471-3118 fax >www.sfm.ne.gov > >the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)