OK. This is a garage below dwelling units. Does 6.7.2 apply or does
6.7.3? 2 allows you to drop the hose stream, etc., but 3 just says
design per 13, which I interpret to mean all of 13, including hose demand.
At 07:24 AM 1/8/2009, you wrote:
Why would you include hose streams in #13R?
Do you include 750 GPM hose on ESFR?
glc
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, January 08, 2009 7:07 AM
To: [email protected]
Subject: RE: Apartment Building
I always include hose on that type of system (unless it is an
impounded water supply with no connections)
At 01:47 AM 1/8/2009, you wrote:
>Watch out! I don't think you can delete hose allowance for the parkade, as
>it is included in the design criteria for 13. Anyway, I have always
included
>it. Can someone else confirm?
>
>Tony
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Ken
Holsopple
>(forum)
>Sent: January 7, 2009 11:12 AM
>To: [email protected]
>Subject: RE: Apartment Building
>
>"Can the garage be protected with a 13 System and the apartments on top be
a
>13R System?"
>
>David,
>
>Depending on the area height limitations allowed by your state building
>code, the entire building could be done per 13R if the parking garage is
for
>use by the tenants of that building and not "open to the public". Keep in
>mind that 13R gives guidance for areas outside the dwelling unit which
would
>be designed similar to a 13 system without things like a hose allowance.
>
>There was a discussion awhile back that might appear in the archives
>pertaining to this very issue you may want to look up.
>
>Best Regards,
>Ken Holsopple
>Design Manager
>Rowe Sprinkler Systems, Inc.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Autry, David
>Sent: Wednesday, January 07, 2009 10:30 AM
>To: [email protected]
>Subject: Apartment Building
>
>I think I know this but I want to verify.
>
>Two story apartment building on top of a parking garage.
>
>Can the garage be protected with a 13 System and the apartments on top be a
>13R System?
>
>David Autry
>Plans Examiner
>Nebraska State Fire Marshal's Office
>246 S. 14th Street
>Lincoln, NE 68508
>402-471-9659
>402-471-3118 fax
>www.sfm.ne.gov
>
>the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut