Douglas, NFPA 17A says you must install a listed UL 300 compliant system but NFPA does not determine what qualifies as such, UL does. If a system is a listed UL 330 compliant system you know it has passed the testing protocols UL has established as a requirement to obtaining the listing. My understanding is that a UL 300 listed system can have a vertical duct run of unlimited length but is limited to 100' for a horizontal run. I have a run that surpasses 100' and so need an alternative. A grease scrubber is an alternative. A sprinklered duct is another alternative. The problem I have is that I can find how to layout the sprinklers in NFPA 13 but I can't find anything that tells me how to calc those sprinklers which are obviously in their very own design area. IFC has related commentary about duct sprinklers for hazardous fume ducts in semi-conductor plants but I don't see how this applies.
On Sat, Jan 24, 2009 at 4:34 PM, douglas hicks <[email protected]> wrote: > Ron, you made me get my copy of NFPA 17 A-2009. There is no mention of > changes to duct protection. But there is a reference to UL 300 - 2005. Is > that the most current UL 300? > > Douglas Hicks > General Fire Equipment Co of Eastern Oregon, Inc > ----- Original Message ----- From: "Ron Greenman" <[email protected]> > To: <[email protected]> > Sent: Saturday, January 24, 2009 9:45 AM > Subject: Re: Calculating sprinklers in horizontal grease ducts > > >> Douglas, >> >> I'm aware of that but in this installation the horizontal length of >> the duct exceeds the new UL requirements pertaining to the length of >> horizontal ducting which may be protected by a UL 300 compliant >> chemical system, hence the sprinklers in the horizontal ducting. Still >> need some calculation guidelines. The only I can find even close is >> for non-materials handling ductwork, i.e.: extraction ducts, is for >> hazardous chemical vapors in the IFC and I don't think that this >> applies. >> >> On Sat, Jan 24, 2009 at 8:15 AM, douglas hicks <[email protected]> wrote: >>> >>> Is this a new install? A new install would, depending on local and state >>> and AHJ and insurance requirements call for a UL 300 suppression system. >>> Or >>> are you concerned about an existing system? >>> Douglas Hicks >>> >>> ----- >> _______________________________________________ >>> Sprinklerforum mailing list >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >>> For Technical Assistance, send an email to: [email protected] >>> > >> Ron Greenman >> at home.... >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> For Technical Assistance, send an email to: [email protected] >> > > > > -------------------------------------------------------------------------------- > > > > No virus found in this incoming message. > Checked by AVG - http://www.avg.com > Version: 8.0.176 / Virus Database: 270.10.13/1912 - Release Date: 1/23/2009 > 6:54 PM > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)