Ron,

How about this, from the 2007 edition of NFPA-13?

11.2.3.4 Special Design Areas.
11.2.3.4.1 Where the design area consists of a building service chute supplied by a separate riser, the maximum number of sprinklers that needs to be calculated is three each with a minimum discharge of 15 gpm (57 L/min).

11.2.3.4.2* Where an area is to be protected by a single line of sprinklers, the design area shall include all sprinklers on the line up to a maximum of seven.

11.2.3.4.3 Sprinklers in ducts as described in Section 7.10 and 8.15.12 shall be hydraulically designed to provide a discharge pressure of not less than 7 psi (0.5 bar) at each sprinkler with all sprinklers within the duct flowing.

I'm not sure, but I think at least some of that applies to what you're describing.