Ron typically if you asked what to design to  I'd say to calc all of the
heads in the duct. Rarely see grease duct with more than 36x36 or 24x48. As
far as density goes I'd calc a .20 but that really won't matter since the
7Psi will flow more than that except in a really large duct. We find in duct
heads to be problematic, as each requires a fire rated access door, and the
heads and duct never seem to be properly cleaned. I'd look for another
alternative.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Sunday, January 25, 2009 9:49 PM
To: [email protected]
Subject: Re: Calculating sprinklers in horizontal grease ducts

Mike,

 ANSWERS IN CAPS

and meet the intent?

ALTHOUGH iIT MAY MEET THE INTENT IT DOESN'T MEET THE LISTING AND THAT'S WHAT
I'M CONCERNED WITH.

Any possibility of the UV duct hood cleaners and reduction of protection,
i.e. what I've heard about the B.C. experience?

THIS IS POSSIBLE--ROTO-CLONE, ELECTROSTATIC PRECIPITATOR, ACTIVATED CHARCOAL
FILTER, ETC., BUT I'D RATHER AVOID THESE EXPENSIVE AND TYPICALLY MAINTENANCE
NEGLECTED DEVICES.

If you use sprinks, can you recommend a "watertight" duct system with enough
slope to take the water to a "safe" place?  Like outside?

GREASE DUCTS ARE WELDED AND THEREFORE GREASE/WATER TIGHT BY DESIGN.
EVERY TURN AND LOW POINT REQUIRES AN INSPECTION/CLEANING ACCESS PLATE (ALSO
GREASE TIGHT) AND WILL THEN EITHER DRAIN BACK TO THE HOOD, AN ELBOW WITH
ACCESS OR OUTSIDE.

I'd calc every one of them....... up to the equivalent design area of the
building.

I'D CALC EVERYONE ALSO BUT WHAT I'M LOOKING FOR IS GUIDANCE ON THE HAZARD
AND/OR DENSITY.

On Sat, Jan 24, 2009 at 7:04 PM, Michael Fitz <[email protected]> wrote:
> Ron,

--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to