if you want a level of comfort after leaving the sprinkler
out of the "heat pump area", why not make sure you
put a sprinkler near the closet opening, or inside
the closet if you are really worried.

if it is a non-combustible enclosed area, not much
is going to burn.  If the H/P catches the closet on fire anyway,
that is what the sprinkler is for, right next to it in the
entry/hallway.

scot deal
excelsior fire engineering

On Sat, Feb 14, 2009 at 7:12 PM, Greg McGahan <[email protected]> wrote:

> I don't know! The point of this question is indeed the difficulty in
> sorting it out. This "area" is not defined as a room, chase, shaft or
> closet. It is not labeled on the drawings and it amounts to the same type of
> area as a plenum under an HVAC unit except that it actually has the fan
> inside the unit which is inside the area.
>
> There is less than 6" of clearance between the unit and the sheetrock or
> concrete (depending on the wall) on 3 sides.
>
> I agree with NFPA, common sense says you don't need a head bas the unit is
> sealed and if the fan catches on fire it has nowhere to go but into the
> living area which is protected. There is no duct, nor opening to anywhere
> except on the face of the unit.
>
> The EOR says no head, NFPA says not sure but common sense says no, and the
> local AHJ, says I don't know - seems like a head in ther outside of the unit
> is not going to do much. But there is nothing definitive about it IMHO.
>
> Greg McGahan
> Operations Manager
>
> Living Water Fire Protection
> 1160 McKenzie Road
> P.O. Box 877
> Cantonment, Florida 32533
> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> Sent: Friday, February 13, 2009 7:27 PM
> To: [email protected]
>  Subject: Re: water source heat pumps
>
> If it is a high rise and these "closets" are not part of a continuous
> rated shaft how could you justify penetrations through the floors?
>
> On Fri, Feb 13, 2009 at 2:06 PM, Todd Williams <[email protected]> wrote:
> > What is the construction of the space? Are there exposed wood joists?
> Other
> > combustible loading? Does the hatch allow a person into the space or
> would
> > all work on the heat pumps have to be reaching through the opening? If it
> is
> > an unaccessible, N/C space, would 8.14.1.2.2 (2002) apply?
> >
> >
> > At 04:08 PM 2/13/2009, you wrote:
> >>
> >> A call to NFPA gets us to here:
> >>
> >> It doesn't fit anywhere to omit protection, but common sense would
> dictate
> >> that it is not required.
> >>
> >> He suggested we try hanging on to 8.15.1.2.1.
> >>
> >> Does anyone have any experience with these?
> >>
> >> Greg McGahan
> >> Operations Manager
> >>
> >> Living Water Fire Protection
> >> 1160 McKenzie Road
> >> P.O. Box 877
> >> Cantonment, Florida 32533
> >> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> >> [email protected]
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Greg
> McGahan
> >> Sent: Friday, February 13, 2009 2:45 PM
> >> To: [email protected]
> >> Subject: RE: water source heat pumps
> >>
> >> Just got more info. The unit sits in a "closet" but there is NO ACCESS
> >> except through a panel on the front of the unit that allows access to
> the
> >> air filter.
> >>
> >> The only questionable fact to me is that there is an electric fan in the
> >> heat pump.
> >>
> >>
> >> Greg McGahan
> >> Operations Manager
> >>
> >> Living Water Fire Protection
> >> 1160 McKenzie Road
> >> P.O. Box 877
> >> Cantonment, Florida 32533
> >> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> >> [email protected]
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of John
> O'Connor
> >> Sent: Friday, February 13, 2009 2:36 PM
> >> To: [email protected]
> >> Subject: RE: water source heat pumps
> >>
> >> Greg,
> >> One drawback that I see is future service work by another contractor,
> >> thinking that the entire floor is isolated by the FCV and having that
> one
> >> LIVE vertical branchline feeding all the utility closets.  Could be a
> >> problem.
> >>
> >> John R. O'Connor
> >> National Fire Sprinklers, Inc.
> >> Nashville  TN
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Greg
> >> McGahan
> >> Sent: Friday, February 13, 2009 1:48 PM
> >> To: [email protected]
> >> Subject: water source heat pumps
> >>
> >> OK gang I need some advice hopefully based on experience.
> >>
> >> We are doing an independent hotel  that is being constructed more like a
> >> typical condominium. In the far end of each unit (room), there is a
> small
> >> enclosed closet without a door, but with a removable cover that houses a
> >> Water Source Heat Pump.
> >>
> >> I have assumed sprinkler will be required up to this point but I am open
> >> to
> >> comments on that. There is NO WAY to get concealed piping to the closet
> at
> >> this time. The Building is 9 Stories tall with separate FCV's on each
> >> floor
> >> etc.
> >>
> >> My Question is can I feed these closets like a shaft from the 1st floor
> >> system all of the way up in order to avoid a lot of grief and trouble to
> >> get
> >> the owner to add soffits in every Unit?
> >>
> >> All comments welcome except those that point out something painfully
> >> obvious
> >> I may be missing.
> >>
> >> Greg McGahan
> >> Operations Manager
> >>
> >> Living Water Fire Protection
> >> 1160 McKenzie Road
> >> P.O. Box 877
> >> Cantonment, Florida 32533
> >> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> >> [email protected]
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
> [email protected]
> >>
> >> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >>
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
> [email protected]
> >>
> >> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
> [email protected]
> >>
> >> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
> [email protected]
> >>
> >> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> >> (Put the word unsubscribe in the subject field)
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, Connecticut
> > www.fpdc.com
> > 860.535.2080  _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>