I haven't understood why the freezer set up for future testing was not the 
standard for all double interlock systems. 

Everyone knows the day the system goes in the server farm operator is not going 
to allow trip tests. When we've asked for a letter from the owner confirming 
testing will be allowed the valve always gets put in. 

Bruce Verhei 

----- Original Message ----- 
From: "Jay Stough" <[email protected]> 
To: [email protected] 
Sent: Friday, February 13, 2009 3:47:47 AM GMT -08:00 US/Canada Pacific 
Subject: Preaction inspections 

For those of you doing inspections, how do you handle preaction systems? 
13.4.3.2.3 says that they should be trip tested fully open every three years 
similar to dry systems. We don't inspect a lot of preaction systems, but all of 
the owners have not let us do a full trip, they are afraid of water leaking out 
of the system on to their equipment. 

Jay Stough 