I thought the quarterly is inspection to verify physical damage 5.2.6 (2008) 
and semiannually is for testing waterflow and pressure switches, the same as 
72.  

 Jay Stough




________________________________
From: Tom Duross <[email protected]>
To: [email protected]
Sent: Friday, February 13, 2009 10:39:19 AM
Subject: RE: Preaction inspections

For those of you testing other than wet systems, how are you handling
quarterly and yearly testing of waterflow switches if you follow the 3 year
cycle on full trips?  We do limited trips on a quarterly basis and full
trips once a year.

Tom

For those of you doing inspections, how do you handle preaction systems?
13.4.3.2.3 says that they should be trip tested fully open every three years
similar to dry systems.  We don't inspect a lot of preaction systems, but
all of the owners have not let us do a full trip, they are afraid of water
leaking out of the system on to their equipment.