I think so and NFPA thinks so, but no one knows so.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, February 13, 2009 4:07 PM
To: [email protected]
Subject: RE: water source heat pumps

What is the construction of the space? Are there exposed wood joists? 
Other combustible loading? Does the hatch allow a person into the 
space or would all work on the heat pumps have to be reaching through 
the opening? If it is an unaccessible, N/C space, would 8.14.1.2.2 
(2002) apply?


At 04:08 PM 2/13/2009, you wrote:
>A call to NFPA gets us to here:
>
>It doesn't fit anywhere to omit protection, but common sense would 
>dictate that it is not required.
>
>He suggested we try hanging on to 8.15.1.2.1.
>
>Does anyone have any experience with these?
>
>Greg McGahan
>Operations Manager
>
>Living Water Fire Protection
>1160 McKenzie Road
>P.O. Box 877
>Cantonment, Florida 32533
>(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>[email protected]
>
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Greg McGahan
>Sent: Friday, February 13, 2009 2:45 PM
>To: [email protected]
>Subject: RE: water source heat pumps
>
>Just got more info. The unit sits in a "closet" but there is NO 
>ACCESS except through a panel on the front of the unit that allows 
>access to the air filter.
>
>The only questionable fact to me is that there is an electric fan in 
>the heat pump.
>
>
>Greg McGahan
>Operations Manager
>
>Living Water Fire Protection
>1160 McKenzie Road
>P.O. Box 877
>Cantonment, Florida 32533
>(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>[email protected]
>
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of John O'Connor
>Sent: Friday, February 13, 2009 2:36 PM
>To: [email protected]
>Subject: RE: water source heat pumps
>
>Greg,
>One drawback that I see is future service work by another contractor,
>thinking that the entire floor is isolated by the FCV and having that one
>LIVE vertical branchline feeding all the utility closets.  Could be a
>problem.
>
>John R. O'Connor
>National Fire Sprinklers, Inc.
>Nashville  TN
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Greg McGahan
>Sent: Friday, February 13, 2009 1:48 PM
>To: [email protected]
>Subject: water source heat pumps
>
>OK gang I need some advice hopefully based on experience.
>
>We are doing an independent hotel  that is being constructed more like a
>typical condominium. In the far end of each unit (room), there is a small
>enclosed closet without a door, but with a removable cover that houses a
>Water Source Heat Pump.
>
>I have assumed sprinkler will be required up to this point but I am open to
>comments on that. There is NO WAY to get concealed piping to the closet at
>this time. The Building is 9 Stories tall with separate FCV's on each floor
>etc.
>
>My Question is can I feed these closets like a shaft from the 1st floor
>system all of the way up in order to avoid a lot of grief and trouble to get
>the owner to add soffits in every Unit?
>
>All comments welcome except those that point out something painfully obvious
>I may be missing.
>
>Greg McGahan
>Operations Manager
>
>Living Water Fire Protection
>1160 McKenzie Road
>P.O. Box 877
>Cantonment, Florida 32533
>(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>[email protected]
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to