Thanks John. I knew there was a missing component in that experiment
but couldn't (read wasn't interested enough) to put my finger on it.
Thermal expansion--makes you go Hmmmmm?

On Thu, Mar 19, 2009 at 4:20 AM, John Drucker <[email protected]> wrote:
> Thermal Expansion & Water Hammer
>
> One of the consequences of installing a backflow prevention assembly on any
> water system is the system becoming a closed system. A closed system is a
> system, which is not open to the atmosphere. A pressurized tank would be a
> closed system, since there is no means for the pressure to escape.
> A water user's system may be considered an open system if there is no
> backflow protection. Water flows from the water supplier into the water
> user's premises through the water meter. Should something cause the pressure
> on the water user's property to increase, water can freely flow back out
> into the water distribution system.
> What can cause the water user's system to increase in pressure?
>
> A common phenomenon, which increases pressure, is thermal expansion. Thermal
> expansion occurs when water in the pipes heats up. This may be due to
> environmental conditions such as a hot room, or it may be caused by a piece
> of water-using equipment that is generating heat. Regardless of what causes
> the water to heat up, when it does it expands and requires more volume. This
> is no problem in an open system, the water flows back through the meter into
> the distribution system. However, when the system is a closed system, which
> occurs when a double check valve assembly or a reduced pressure principle
> assembly is installed; the water doesn't have anywhere to go. In these
> conditions the pressure can increase dramatically.
>
> Another phenomenon occurring in hydraulic systems is a water hammer. A water
> hammer occurs when the flow of water through a pipe is stopped quickly. This
> may occur because of a solenoid valve, or even a quarter-turn ball valve
> being closed too quickly. The flowing water is stopped when it hits the
> closed valve, but a shock wave is sent back in the opposite direction.
> Again, this wave would dissipate if the system was an open system. However,
> in a system, which is closed, because of a backflow preventer, the shock
> wave will hit the downstream check valve of the backflow preventer and the
> wave will move back throughout the system. This may increase the pressure
> throughout the system up to several times the normal water pressure. This is
> enough to cause significant damage in equipment and water fixtures. In a
> mathematical model, water flowing at 15 feet per second through pipe
> generated an increase in pressure of over 900 pounds per square inch (psi),
> when a downstream valve was closed instantaneously.
> What can be done to prevent damage in a system subjected to either water
> hammer or thermal expansion?
>
> Expansion Tank
> Under the thermal expansion situation described above, the system could be
> protected by the installation of an expansion tank. An expansion tank is
> attached to the water system and may be pressurized with air on one side of
> a diaphragm within the tank. When the water pressure increases due to
> thermal expansion, the tank begins tfill with water pressurizing the air on
> the other side of the diaphragm. Water is not compressible, so when the
> water begins to expand due to heat, it needs to go somewhere. Air on the
> other hand is compressible. So, the expanded water goes into one side of the
> tank compressing the air on the other side. This prevents any part of the
> system from giving way to the expanding water.
>
> Although an expansion tank may help solve a thermal expansion problem, water
> hammer may be so powerful that an expansion tank won't take care of the
> problem. A water hammer arrester may be installed to reduce the effects of
> the water hammer. In some cases some re-engineering of the system may be
> necessary. For example, at the industrial complex, the solenoid valve was
> adjusted to close very slowly. So, instead of closing nearly
> instantaneously, the closure was very slow and thus, the water hammer was
> eliminated.
>
> Courtesy of the USC School of Engineering
> Foundation for Cross-Connection Control and Hydraulic Research
> http://www.wvdhhr.org/phs/water/Thermal_Expansion.pdf
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Rodney Hamm
> Sent: Wednesday, March 18, 2009 9:23 PM
> To: [email protected]
> Subject: Excessive system pressure
>
> I find it VERY interesting that it has been over a week since I
> suggested/challenged the forum participants to a simple experiment and there
> has been exactly ZERO responses to report any conclusions/findings.
>
>
>
> I am wondering if anyone actually tried the experiment referenced
> below....if so, I wonder why has there been no response through the forum?
> Could it be that some have spent the 4-5 minutes and have decided against
> posting a response because the experiment does not support their theory?
> Could it possibly be that the various forum participants who believe water
> compression is the root cause of high system pressures are to "old school"
> and "close minded" (to use a phrase that was used to describe me..heh heh
> heh..really funny if you knew me at all) to consider a simple experiment
> that might in any way challenge their way of thinking? Or could it possibly
> be that water and air act differently to temperature changes in Georgia than
> any other place in the world?
>
>
>
> I am having a little too much fun with this email.
>
>
>
> On a more serious note, I was at another plant yesterday which has the same
> exact problem. This is really why I am writing this email. Warehouse with 1
> gridded system and 7 tree fed systems. The problem only exists for the
> gridded system; the remaining 7 systems had nominal pressure differences
> (0-10 psi difference) between the top & bottom gauges. On the gridded
> system, the public pressure upstream of the alarm check valve was fairly
> steady all afternoon at ~60 psi. At 1:50 PM, the system pressure downstream
> of the alarm check valve was 190 psi. I described the problem to the plant
> engineer and he wanted me to explain the problem to the plant manager. The
> three of us returned to the riser at 2:10 PM and the system pressure
> downstream of the alarm check valve was already up to 205 psi. We have not
> even entered our really hot days of summer yet! Riser nipples on the near
> main and the far main and the ITC for the system was attached to the bottom
> of the far main (in other words, the auxiliary or low point drain was
> converted into an ITC by installing the base of a sprinkler head at the end
> of the pipe and then someone placed an ITC sign on the valve). This system
> was installed prior to the NFPA requirement of a 175 psi PRV for all gridded
> systems. I have recommended the provision of a 175 psi PRV, installing air
> bleed off valves and removing a significant amount of the trapped air from
> the system. The ITC piping "SHOULD" be arranged to flow water through the
> highest point of the system whenever possible, but some people just don't
> give a damn!
>
>
>
>
>
> Rodney K. Hamm, P.E.
> President/Owner
> Falcon Fire Protection
> Office  (478) 953-1677
>
> Cell  (478) 396-6988
>
>
>
> Date: Wed, 11 Mar 2009 15:47:19 -0400
>
> From: "Rodney Hamm" <[email protected]>
>
> Subject: RE: Test/Drain at the Riser
>
> To: <[email protected]>
>
> Message-ID: <[email protected]>
>
> Content-Type: text/plain;     charset="us-ascii"
>
>
>
> I challenge you to try my suggested experiment! Even if you do not want to
> try it..try it with a preconceived notion that I am completely wrong.
>
>
>
> Take a completely 100% full glass of cold water (plastic would be best) pull
> some saran wrap over the top very tight and add a rubber band really tight
> to make sure no air leaks out. Make sure there are no air bubbles on top.
> Put the full glass of water in the microwave on HIGH for 2 minutes. No
> pressure builds up inside the glass because water is not compressible and
> does not expand. Pressure will eventually build if you let the water start
> to boil. THEN do the same exact thing with a glass half full of cold water.
> Using saran wrap and a tight rubber band, you will see the pressure
> increases dramatically and eventually will burst the saran wrap after the
> balloon effect!
>
>
>
> The results will be so obvious you will see my point. The plastic film on
> top allows you to see the dramatic difference in pressure increase (100%
> water vs. 50% air). My experiment is actually a closed system. I will agree
> that the volume is allowed to increase, but the only force which allows the
> plastic film to balloon is due to the increased pressure in the closed
> container. If the same percentage of water/air was in a sprinkler pipe, the
> increased pressure caused by the temperature increase would cause the system
> pressure to increase dramatically due to the fact that there is no change in
> volume (until a leak or system rupture occurs). Of course, the best test
> environment would be to use a sprinkler system in an oven with a calibrated
> pressure gauge, but most of our forum readers would never take this much
> time and effort. The experiment I suggested is VERY convincing if you are
> willing to spend 5 minutes of your time to try.
>
>
>
> Air is compressible and water is not compressible. Temperature increases or
> decreases do not affect the pressure of a section of pipe filled with 100%
> water until the water begins to boil. Temperature increases will cause the
> pressure to increase if the same section of pipe is filled with air or has a
> significant percentage of air along with some water. Temperature decreases
> will cause the pressure to decrease if the same section of pipe is filled
> with air or has a significant percentage of air along with some water.
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to