I believe you still must use residential sprinklers IF it is residential. I
do not know of any listed for dry use. You may have to cover the pipe and
use listed attic sprinklers to protect any CPVC and the like, and run it
wet.

R/
Matt

 
Matthew J. Willis
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Arthur Tiroly
Sent: Monday, March 30, 2009 9:52 AM
To: [email protected]
Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM

The top floor residential suits are supplied by the dry system in the attic.
My main question - does the time delay compromise the life safety of the
elderly housing residential occupants?

Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Monday, March 30, 2009 10:46 AM
To: [email protected]
Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM

The dry system in the attic falls under 13, 13R allows the omission. If 13
is specified, that may be the reason why. I have seen and done it in nursing
homes. Also you will see this in 4 story and under hotel/motels depending on
owner.

R/
Matt


Matthew J. Willis
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Arthur Tiroly
Sent: Monday, March 30, 2009 9:38 AM
To: [email protected]
Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM

It is my understanding that sprinklers in an elderly housing assisted living
apartment facility is primarily life safety.

Can a large dry system installed in an attic with the usual time delays of
water delivered to the end head compromise the life safety aspect of the
sprinkler system?
The attic has 2 large air handlers with gas fired heating + AC and is fully
sprinklered but considered unheated.

It is just 2 stories and 13R could be used but 13 is specified. Is the dry
system acceptable for life safety?

Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to