I believe that most "Nursing Homes" fall under light hazard, not residential. This is significant with dry systems since the water delivery time is very different.
Table 7.2.3.6.1 Dry System Water Delivery Hazard Number of Most Remote Sprinklers Initially Open Maximum Time of Water Delivery Residential 1head 15 seconds Light 1head 60 seconds Ordinary I 2heads 50 seconds Ordinary II 2heads 50 seconds Extra I 4heads 45 seconds Extra II 4heads 45 seconds High piled 4heads 40 seconds Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matthew J. Willis Sent: Monday, March 30, 2009 8:55 AM To: [email protected] Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM I believe you still must use residential sprinklers IF it is residential. I do not know of any listed for dry use. You may have to cover the pipe and use listed attic sprinklers to protect any CPVC and the like, and run it wet. R/ Matt Matthew J. Willis Norred Fire Systems L.L.C. 318-387-1134 Voice 318-387-1163 Facsimile [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Arthur Tiroly Sent: Monday, March 30, 2009 9:52 AM To: [email protected] Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM The top floor residential suits are supplied by the dry system in the attic. My main question - does the time delay compromise the life safety of the elderly housing residential occupants? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 3300 King Ave Cleveland, OH 44114 216-621-8899 216-570-7030 cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matthew J. Willis Sent: Monday, March 30, 2009 10:46 AM To: [email protected] Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM The dry system in the attic falls under 13, 13R allows the omission. If 13 is specified, that may be the reason why. I have seen and done it in nursing homes. Also you will see this in 4 story and under hotel/motels depending on owner. R/ Matt Matthew J. Willis Norred Fire Systems L.L.C. 318-387-1134 Voice 318-387-1163 Facsimile [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Arthur Tiroly Sent: Monday, March 30, 2009 9:38 AM To: [email protected] Subject: RE: RESIDENTIAL OCCOPANCY DRY SYSTEM It is my understanding that sprinklers in an elderly housing assisted living apartment facility is primarily life safety. Can a large dry system installed in an attic with the usual time delays of water delivered to the end head compromise the life safety aspect of the sprinkler system? The attic has 2 large air handlers with gas fired heating + AC and is fully sprinklered but considered unheated. It is just 2 stories and 13R could be used but 13 is specified. Is the dry system acceptable for life safety? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 3300 King Ave Cleveland, OH 44114 216-621-8899 216-570-7030 cell _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)