I wasn't thinking static test, I was thinking actual water flow

At 05:25 PM 5/15/2009, you wrote:
>Same here! We test all of our systems including the FDC to 200/2hrs. If it
>has an FDC your required to test same as all 13, even if 13D.
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Charles
>Thurston
>Sent: Friday, May 15, 2009 1:18 PM
>To: Todd Williams
>Subject: Re[2]: CPVC w/o water between riser and FDC
>
>Hello Todd,
>
>We pump into em with 200 for the final with no problems. Last one was about
>90 feet underground.
>
>Friday, May 15, 2009, 2:43:55 PM, you wrote:
>
> > Has anybody tried pumping 150 psi into an FDC piped with 40 ft of
> > CPVC? Are there water hammer issues? Can the glued fittings handle it?
> > Any additional restraint required? The listing issue may be one thing,
> > but the actual installation may have some unforeseen consequences.
>
>
>
> > At 02:28 PM 5/15/2009, you wrote:
> >>As Long as the pipe is not exposed or if it is it meets the normal
> >>restrictions for cpvc, it should be ok.
> >>
> >>Thom McMahon, SET
> >>Firetech, Inc.
> >>2560 Copper Ridge Dr
> >>P.O. Box 882136
> >>Steamboat Springs, CO 80488
> >>Tel:  970-879-7952
> >>Fax: 970-879-7926
> >>
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of R
> >>Richardson
> >>Sent: Friday, May 15, 2009 12:25 PM
> >>To: [email protected]
> >>Subject: RE: CPVC w/o water between riser and FDC
> >>
> >>In this particular case it is a run of about 40 ft. through some
> >>sprinklered rooms.  Still seems OK?
> >>
> >>Rich Richardson
> >>Seattle Fire Department
> >>
> >> >>> "Steve Leyton" <[email protected]> 05/15/2009 10:07 >>>
> >>We have never been concerned with this and I'd say it's standard
> >>practice on most 13R systems throughout the Southwest.   It's generally
> >>a short run of pipe if the FDC is on the wall.
> >>
> >>Steve Leyton
> >>Protection Design & Consulting
> >>San Diego, CA
> >>
> >>
> >>
> >>
> >>-----Original Message-----
> >>From: [email protected]
> >>[mailto:[email protected]] On Behalf Of R
> >>Richardson
> >>Sent: Friday, May 15, 2009 10:04 AM
> >>To: [email protected]
> >>Subject: CPVC w/o water between riser and FDC
> >>
> >>We are reviewing a proposal for a wet pipe sprinkler system using CPVC
>pipe.
> >>However, there is a run of CPVC pipe between the FDC and the riser
> >>that is dry, is this standard practice or acceptable?
> >>
> >>Thanks,
> >>
> >>Rich Richardson
> >>Seattle Fire Department
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>
> >>__________ Information from ESET NOD32 Antivirus, version of virus
> >>signature database 4080 (20090515) __________
> >>
> >>The message was checked by ESET NOD32 Antivirus.
> >>
> >>http://www.eset.com
> >>
> >>
> >>
> >>__________ Information from ESET NOD32 Antivirus, version of virus
> >>signature database 4080 (20090515) __________
> >>
> >>The message was checked by ESET NOD32 Antivirus.
> >>
> >>http://www.eset.com
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>For Technical Assistance, send an email to:
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
>
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, Connecticut
> > www.fpdc.com
> > 860.535.2080
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> > [email protected]
>
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
>
>
>--
>Best regards,
>  Charles Thurston                            mailto:[email protected]
>   Coastal Fire Protection
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to