Is the clubhouse for residents only or for the general public? Is the 
Clubhouse considered to be "incidental" to the residential occupancy? 
The real interesting question would come if the apartment/clubhouse 
was part of a multi-building complex and the Clubhouse was only for 
residents of the complex. NFPA 13R section A1.1 covers this a little.


At 12:19 PM 5/29/2009, you wrote:
>How about this scenario for a building with 13 and 13R systems in ICC land:
>
>
>
>4 story residential building with attached clubhouse on 1st floor (non-fire
>wall separation between clubhouse).  Clubhouse is an A3 occupancy with an
>occupant load exceeding 300.   R occupancy requires 13R system however the
>A3 occupancy requires a 13 system throughout the "fire area" only per 06 IFC
>903.2.1.3.  The 13 system would be provided throughout the 1st floor
>(including combustible concealed floor/ceiling assembly) above the 1st floor
>is another fire area and therefore would be 13R above.
>
>
>
>Yes, no?
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  