We did loops, and while the main filled, all the branch lines that did not
have open orifices remained basically empty under equalized pressure. 

Hey; Ken are you out there? Jump in any time!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Sunday, May 03, 2009 11:36 AM
To: [email protected]
Subject: Re: Slow responding dry pipe valves

Thom,

Counter intuitive until visualized (my visualization being your
description). This makes perfect sense on trees (I can really "see"
what you're describing). My "picture" with a grid is just the opposite (what
intuition would expect you to "see"). My "visual" for loops is vague, like
looking through the fog, but is tending towards the tree picture. Now I
haven't bought your story completely (computer models
notwithstanding) but I do like to have my notions challenged.

On Sun, May 3, 2009 at 10:15 AM, Thom McMahon <[email protected]>
wrote:
> Frans:
>
> I know this is not germane to your problem, but it is a reason I do 
> not spec or use low pressure air DPV's.
>
> While visiting Rowe sprinkler I had the opportunity to have their lead 
> designer show me how Counter Intuitive the air supply is using the 
> water delivery time software from TYCO. We were able to run delivery 
> time on several different systems at various air pressures in a few short
minutes.
> We could watch the graphic water display on the monitor which even 
> showed the water compression bounce on dead end branch line. It was an 
> amazing experience to actually see what was happening as the air 
> exhausted from just one or two heads.
>
> Long story getting longer, basically the delivery time was a lot 
> shorter in the higher air pressure system than in a low air pressure 
> system, because you had to "FILL" less of the HP system with water 
> before it came out the open orifice.
>
> Basically our dry systems here operate on a much higher air pressure, 
> because of our high incoming water pressures. That combined with the 
> high Altitude, make our air compressors work harder. (Burn Out 
> sooner.) but our delivery times work.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to