Obstructed velocity check valve might be a contributing factor. Confirm the
velocity check valve seals properly when the accelerator initially trips.
The accelerator trip should occur much faster than 50 seconds as long as the
air supply from the compressor is properly restricted (rather than set for
full flow fill mode as described below). If the velocity check valve does
not seal when the accelerator activates, air pressure does not accumulate in
the intermediate chamber...this significantly reduces the effectiveness and
operational functionality of the accelerator. I have seen and resolved this
problem several times. 

 

Ask the people who witnessed the previous trip tests if the DPV tripped the
very instance (or within 1-2 seconds) after the accelerator activated. If
the accelerator activated at ~12 seconds and ~16 psi and the DPV tripped at
50 seconds after the system pressure reached a significantly lower pressure,
you might have air escaping through the velocity check valve rather than
building pressure in the intermediate chamber. 

 

Good luck!

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

Date: Sun, 3 May 2009 08:58:21 -0700

From: Ron Greenman <[email protected]>

Subject: Re: Slow responding dry pipe valves

To: [email protected]

Message-ID:

      <[email protected]>

Content-Type: text/plain; charset=ISO-8859-1

 

Frans,

 

I was going to suggest that the air maintenance device might be faulty

but David beat me. Not only is he smarter than I am but he's quicker.

I had a similar problem on a giant system with four exhausters once.

(This was a SeaLand warehouse and I seem to remember there was a

horizon between one end and the other :-}). Apart from the exhausters

being a maintenance nightmare they were operating as Ed described even

when working. Similar pressures were also at play. The system was

large but with a lot of small pipes with screwed ends layed out in a

similar fashion to a pipe schedule with diminishing sizes towards the

end. The problem was a stone in the branch line several joints back

from the IT where a transition in size had occurred. Bon Chance.

 

On Sat, May 2, 2009 at 10:25 PM, David de Vries

<[email protected]> wrote:

> Yes, that 50 second trip time with the new accelerator still appears too
long.? Is the air maintenace device working properly?? Perhaps left in fill
mode rather than switched to operating mode?? Or the orifice is missing from
the operating side of the AMD?

> 

> Dave

> 

> David A. de Vries, P.E., CSP

> Firetech Engineering Incorporated

> 

> 

> --- On Sat, 5/2/09, Ed Vining <[email protected]> wrote:

> 

> 

> From: Ed Vining <[email protected]>

> Subject: Re: Slow responding dry pipe valves

> To: [email protected]

> Date: Saturday, May 2, 2009, 10:08 PM

> 

> 

> You point out that the valve now trips in 50 seconds, where before it was

> 80. This indicates the accelerator is working, but not fast enough.

> Possibly because of the accelerator itself.? A restriction in the IT

> discharge line could cause it too.? If the pipe to the ITV is very long,

> trip time could be reduced by upping the size.? Even if the accelerator

> tripped much faster, it seems the delivery time would be too long

> 

> An exhauster would certainly help, particularly if it is way out on the

> system.? One has to be careful, though, when both an exhauster and

> accelerator are used.? The exhauster must trip first.

> 

> A manufacturer could tell you if the 19 psi is outside the working range
of

> his exhauster.? Spec sheets usually list only the maximum rated pressure.

> The speed of operation of an exhauster can be adjusted, but it must be
done

> carefully.? If it is too sensitive, the system could trip on normal

> variations in pressure.

> 

> Ed

> 

> --

> Ed Vining

> 4819 John Muir Rd

> Martinez CA 94553

> 925-228-8792

 