Grab the hanger, not the pipe. Another reason to have smooth edges on CPVC
hangers!

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, August 04, 2009 11:10 AM
To: [email protected]
Subject: RE: trapeze hanger, PVC

Something to think about. Hangers are designed to take 5x wt of water 
filled pipe +250 lbs. The 250 is supposedly to support a fitter if he 
had to grab on to it in an emergency (or so I have been told). Has 
anyone looked into if CPVC pipe could support a 250 lb person, even 
with hangers designed for it?



At 10:54 AM 8/4/2009, you wrote:
>Why not just calculate the modulus using the methods in NFPA 13 and then
>size your trapeze pipe accordingly.  Or, as George said, use the values
>for steel and just have some oversized trapeze bars.
>
> > Assuming CPVC weighs less than steel pipe, use values for steel and
you're
> > safe. If you're near a head, make sure you're protecting against upward
> > movement if needed.
> >
> > When we get into bar joist construction, we often switch to steel since
> > hanging issues often make it a better installation all around.
> >
> > glc
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > [email protected]
> > Sent: Tuesday, August 04, 2009 9:03 AM
> > To: [email protected]
> > Subject: Re: trapeze hanger, PVC
> >
> > Greg,
> > If you are in a position to require trapeze hangers on cpvc,maybe you
need
> > to reconsider using steel pipe for stability and rigidity.Just a
thought.
> > ---- Greg McGahan <[email protected]> wrote:
> >> Have we ever discussed the use of trapeze hangers for cpvc piping?
> > Specifically, modulus requirements etc?
> >>
> >> Greg McGahan
> >> Operations Manager
> >>
> >> Living Water Fire Protection
> >> 1160 McKenzie Road
> >> P.O. Box 877
> >> Cantonment, Florida 32533
> >> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> >> [email protected]
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
> >> [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>--
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to