Even with steel pipe, you may find that you need to grab the hanger and not
the pipe. I did a simple empirical  test with a 1'' pipe supported at
maximum spacings a few inches above the ground with a threaded tee in the
centre. Had a 220# plus guy stand on it and found that the pipe deformed
severely at the joints. (Can't remember if it snapped.)

This was to prove that the requirement of the standard is for the hangers
to be able to carry the 250# load and not the pipe.

Regards




Chris Mak
Sprinkler Certification Manager
Aon New Zealand
Level 1, 4 Fred Thomas Drive,, Takapuna

DDI: +64 9 486 9761  | Mobile:027 434 4058  | Fax:+64 9 486 0112



                                                                       
             "George Church"                                           
             <[email protected]>                                          
             Sent by:                                                   To
             sprinklerforum-bo         <[email protected]>
             un...@firesprinkl                                          cc
             er.org                                                    
                                                                   Subject
                                       RE: trapeze hanger, PVC         
             05/08/2009 03:46                                          
             a.m.                                                      
                                                                       
                                                                       
             Please respond to                                         
             sprinklerfo...@fi                                         
              resprinkler.org                                          
                                                                       
                                                                       




Grab the hanger, not the pipe. Another reason to have smooth edges on CPVC
hangers!

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Tuesday, August 04, 2009 11:10 AM
To: [email protected]
Subject: RE: trapeze hanger, PVC

Something to think about. Hangers are designed to take 5x wt of water
filled pipe +250 lbs. The 250 is supposedly to support a fitter if he
had to grab on to it in an emergency (or so I have been told). Has
anyone looked into if CPVC pipe could support a 250 lb person, even
with hangers designed for it?



At 10:54 AM 8/4/2009, you wrote:
>Why not just calculate the modulus using the methods in NFPA 13 and then
>size your trapeze pipe accordingly.  Or, as George said, use the values
>for steel and just have some oversized trapeze bars.
>
> > Assuming CPVC weighs less than steel pipe, use values for steel and
you're
> > safe. If you're near a head, make sure you're protecting against upward
> > movement if needed.
> >
> > When we get into bar joist construction, we often switch to steel since
> > hanging issues often make it a better installation all around.
> >
> > glc
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > [email protected]
> > Sent: Tuesday, August 04, 2009 9:03 AM
> > To: [email protected]
> > Subject: Re: trapeze hanger, PVC
> >
> > Greg,
> > If you are in a position to require trapeze hangers on cpvc,maybe you
need
> > to reconsider using steel pipe for stability and rigidity.Just a
thought.
> > ---- Greg McGahan <[email protected]> wrote:
> >> Have we ever discussed the use of trapeze hangers for cpvc piping?
> > Specifically, modulus requirements etc?
> >>
> >> Greg McGahan
> >> Operations Manager
> >>
> >> Living Water Fire Protection
> >> 1160 McKenzie Road
> >> P.O. Box 877
> >> Cantonment, Florida 32533
> >> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> >> [email protected]
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
> >> [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
[email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>--
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


This document should only be read by those persons to whom it is addressed and 
is not intended to be relied upon by any person without subsequent written 
confirmation of its contents. Accordingly, our company disclaim all 
responsibility and accept no liability (including in negligence) for the 
consequences for any person acting, or refraining from acting, on such 
information prior to the receipt by those persons of subsequent written 
confirmation.

If you have received this e-mail message in error, please notify us immediately 
by telephone. Please also destroy and delete the message from your computer. 
The Unsolicited Electronic Message Act 2007 (The Spam Act) came into effect 
from 5 September 2007. As a valued client you may receive communications from 
us from time to time, including electronic publications, invitations and 
related information. Please advise if you wish us to stop sending these 
communications to you. Otherwise we will assume you wish to continue receiving 
these communications from us. 

Any form of reproduction, dissemination, copying, disclosure, modification, 
distribution and/or publication of this e-mail message is strictly prohibited.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to