So? If the "fitter, ceiling cleaner or other worker" was to tie off his OSHA
required fall protection. (I know OSHA say's "Structure") But since we keep
designing it to hold and extra 250# it looks solid enough to tie onto. So
when this worker falls his 6'-0" max his impact load is something like
3800#. More likely than a nice gentle giant slowly applying his weight to
the pipe? Should the committee also add "and impact load for fall
protection" to the standard? 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, August 04, 2009 2:14 PM
To: [email protected]
Subject: Re: trapeze hanger, PVC

Actually the fitter story is referenced in the Handbook commentary 
(9.1.1.2 - 2002)


At 11:39 AM 8/4/2009, you wrote:
>I don't know if that extra 250 lbs was really for the fitter of old to
>grab onto or if that is just the story we've been telling each other
>for so long it's become the common "truth." 