So? If the "fitter, ceiling cleaner or other worker" was to tie off his OSHA required fall protection. (I know OSHA say's "Structure") But since we keep designing it to hold and extra 250# it looks solid enough to tie onto. So when this worker falls his 6'-0" max his impact load is something like 3800#. More likely than a nice gentle giant slowly applying his weight to the pipe? Should the committee also add "and impact load for fall protection" to the standard?
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Tuesday, August 04, 2009 2:14 PM To: [email protected] Subject: Re: trapeze hanger, PVC Actually the fitter story is referenced in the Handbook commentary (9.1.1.2 - 2002) At 11:39 AM 8/4/2009, you wrote: >I don't know if that extra 250 lbs was really for the fitter of old to >grab onto or if that is just the story we've been telling each other >for so long it's become the common "truth." _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)