NFPA 13, 2007

8.4.7.2* Galvanized Pipe.
8.4.7.2.1 Where steel pipe is used in preaction and dry pipe
systems, piping materials shall be limited to internally galvanized
steel.
8.4.7.2.2 Nongalvanized fittings shall be permitted. 

Preaction and dry systems are very similar in nature with a few exceptions.  
Both under normal operating conditions have no water in their piping.  
Preaction is a bit more complicated due to supervision of the piping and 
separate detection devices which evoke an opening of the preaction valve.  Dry 
systems are setup to respond to the opening of a sprinkler head.  Preaction 
systems, depending on what type you specify may require multiple steps before 
permitting water into the piping.

There are multiple references in 13 where preaction systems are to be 
classified as dry systems, depending on type of sprinklers used and other 
factors.  Look at 14.3.7.1, 15.3.6 for example.




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Eladio N. 
Alvarado
Sent: Wednesday, September 09, 2009 9:05 AM
To: Sprinklerforum
Subject: Galvanized Pipe

Would someone be good enough to direct me to the specific location where 
Galvanized pipe is required by 13 for Dry systems? And where it may be 
indicated that Pre-action systems are considered "Dry". I've been trying to 
find it on the On-line codes but I seem to be having trouble dealing with their 
search engine. Any help would be greatly appreciated.


Eladio Alvarado
AFSDII




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to