Actually, it weekly/monthly.  Does anyone have a contract to go and
inspect an electrically supervised or locked valves on a monthly basis?

13.3.2 Inspection.
13.3.2.1 All valves shall be inspected weekly.
13.3.2.1.1 Valves secured with locks or supervised in accordance with
applicable NFPA standards shall be permitted to be inspected monthly.

Possibly a big part of the problematic wording of NFPA 25 is that it
originated from NFPA 13A which was a recommended practice that seemingly
was written more for the system owner to ensure that his system worked.

I assume that changing the shoulds to shalls and making it a code really
puts the ITM folks in a bind because it wasn't written to limit
liability of the maintainer, but to actually ensure that the system
worked to provide property protection and life safety.

Maybe it is time to write a new ITM standard that limits the liability
of the ITM folks and only checks the operational status of the
components, which is where we seem to be going in NFPA 25 and a then
write a new document that would actually ensure that the system works as
intended/required for the hazards involved using "qualified" competent
contractors who not only are capable doing ITM but designing the system
as well.

We can't water down the requirements of NFPA 25 to eliminate ITM
contractor liability and still meet the purpose of the standard as it is
now written.

1.2* Purpose. The purpose of this document is to provide requirements
that ensure a reasonable degree of protection for life and property from
fire through minimum inspection, testing, and maintenance methods for
water-based fire protection systems. In those cases where it is
determined that an existing situation involves a distinct hazard to life
or property, the authority having jurisdiction shall be permitted to
require inspection, testing, and maintenance methods in excess of those
required by the standard.

We've had a fire where an Omega did not operate in a patient room.  When
a standard is written such that a contractor has to go out of his way to
write a certified letter to let us know that the sprinkler that he is
already required to inspect is actually a recalled head and should be
addressed, then the standard is severely broken!

PL
   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest
Wilson
Sent: Monday, September 21, 2009 6:30 PM
To: [email protected]
Subject: RE: NFPA 25 and Scope

Regarding chain vs electrical tampers, inspection frequency should also 
be considered in the decision process. If I recall correctly, chain and 
lock valves must be inspected weekly per 25. Electric tampers are 
quarterly?


Forest Wilson

Project Manager
Cherokee Fire Protection Co.
3195 Dayton Xenia Rd Ste 900
Dayton OH 45434

ph: 937-376-2333
fx: 614-455-4324
cell: 937-307-5647


.



Visit our blog: www.cherokee-fire.blogspot.com







NOTICE: The information contained in this email is intended to be 
solely for the use of the named individual or entity to which it is 
directed and may contain information that is privileged or otherwise 
confidential. It is not intended for transmission to, or receipt by, 
anyone other than the named addressee (or a person authorized to 
deliver it to the named addressee). It should not be copied or 
forwarded to any unauthorized persons. If you have received this 
electronic mail transmission in error, please delete it from your 
system without copying or forwarding it, and notify the sender of the 
error by reply email or by calling Cherokee Fire Protection Co. at 
888-347-3079 toll free.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to