>>>>>The IBC (2003) section 903.4 required electronic supervision and does
not have an exception for locked or sealed. So if it is locked and
not supervised, you may meet NFPA requirements but not IBC. Now the
question comes up. If you are doing and NFPA 25 inspection, are you
just doing it to NFPA standards or to the local building/fire codes as well?


The inspection is done per 25. Nothing in 13, IBC, or anything else comes
into play. Which is why if I see a lock, I will green tag.
If I see nothing, and price the correction, I do so per ALL applicable
codes. My thinking is the later liability of pricing something that does not
meet code. With the inspection, we are covered if we stay within the
guidelines of 25. But for corrections, I think it is a different matter.