I believe 8.6.4.1.1.3 is referring to a ceiling elevation change where heads 
must be installed below the lower elevation due to the area and distance from 
the adjacent wall.  To put it another way, the elevation change is out in the 
middle of a larger room where D from figure 8.6.5.1.2(b) is > than 30" 
therefore the head must be in the lower elevated lid. A ceiling is not an 
obstruction in my opinion.  A soffit on the other hand is.  A soffit is more 
closely defined by an obstruction as shown in 8.6.5.1.2(b).  I believe 
8.6.4.1.1.3 is to be followed when it is already established that a head is 
required under that lower lid as indicated when it states "...the sprinklers 
shall be permitted to be spaced as though the ceiling was flat, therefore, 
follow 8.6.4.1.1.3 in that scenario.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, September 23, 2009 9:31 AM
To: [email protected]
Subject: RE: bar backs

BUT

(A)    Where a vertical change in ceiling elevation within the area of coverage 
of the sprinkler creates a distance of more than 36 in. (914 mm) between the 
upper ceiling and the sprinkler deflector, a vertical plane extending down from 
the ceiling at the change in elevation shall be considered a wall for the 
purpose of sprinkler spacing as shown in Figure 8.6.4.1.1.3(A). 

According to the new rule I believe that we cannot use the obstruction rules.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bryan Dann
Sent: Wednesday, September 23, 2009 9:25 AM
To: [email protected]
Subject: RE: bar backs

Take a look at Figure 8.6.5.1(b)  page 13-57 NFPA 13(07)

If head can be 4'6 away from obstruction your ok.

Bryan A. Dann
Dannba Design Services, LLC
Fire Sprinkler Designs
Office: (740) 363-5878
Cell: (740) 803-0967
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, September 23, 2009 9:59 AM
To: [email protected]
Subject: bar backs


I have seen dozens if not hundreds of similar situation without sprinklers
and just wanted to get the professional spin on it:

The area behind a bar where the liquor is kept has a ceiling height of 9-6
and the remainder if the Bar is at 13'-0". Of course the "soffit" is about
1'-9" wide.

My thoughts are that a head is required due to the difference in elevation
being greater than 3'-0".

Any other thoughts?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to