I wonder if the IBC defines a "water curtain" ?
If it were in the NFPA Manual of style, it'd be in Ch 3.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Blackwell
Sent: Wednesday, September 23, 2009 3:39 PM
To: [email protected]
Subject: RE: Water curtains for windows

 

That "someone" is the ICC.  Here is where the water curtains are
mentioned in the 2006 IBC:

 

704.12 Opening protection. Windows in exterior walls

required to have protected openings in accordance with other

sections of this code or determined to be protected in accordance

with Section 704.3 or 704.8 shall comply with Section

715.5. Other openings required to be protected with fire door or

shutter assemblies in accordance with other sections of this

code or determined to be protected in accordance with Section

704.3 or 704.8 shall comply with Section 715.4.

Exception: Opening protectives are not required where the

building is protected throughout by an automatic sprinkler

system and the exterior openings are protected by an

approved water curtain using automatic sprinklers approved

for that use. The sprinklers and the water curtain shall be

installed in accordance with Section 903.3.1.1 and shall

have an automatic water supply and fire department connection.

 

 

410.3.5 Proscenium curtain. Where a proscenium wall is

required to have a fire-resistance rating, the stage opening

shall be provided with a fire curtain of approved material or

an approved water curtain complying with Section

903.3.1.1. The fire curtain shall be designed and installed to

intercept hot gases, flames and smoke and to prevent a glow

from a severe fire on the stage from showing on the auditorium

side for a period of 20 minutes. The closing of the fire

curtain from the full open position shall be accomplished in

less than 30 seconds, with the last 8 feet (2438 mm) of travel

requiring 5 or more seconds for full closure.

 

 

 

 

David W. S. Blackwell, II, PE, CFI-I, CFPE

Engineering 

---------------------------------------------------------------- 

Office of State Fire Marshal 

141 Monticello Trail 

Columbia, SC 29203 

Phone:  803.896.9833 

Fax:  803.896.9806 

Email:  [email protected] 

OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 

---------------------------------------------------------------- 

 

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom
Duross
Sent: Wednesday, September 23, 2009 3:17 PM
To: [email protected]
Subject: RE: Water curtains for windows

 

Maybe the same folks that told them dry sidewalls work for exposure

protection.

 

TD

 

Somewhere, somehow, somebody told some architects and engineers that
they

can use water curtains in lieu of fire-rated construction.

 

David Autry

Plans Examiner

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 

For Technical Assistance, send an email to: [email protected]

 

To Unsubscribe, send an email
to:[email protected]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to