Let me rephrase for Ralphy.  Last week we spoke about failure causes.  What
I think he is trying to convey is if the valve is open statistically nothing
else matters.  OK it's not that simple but 3-5 lbs under on a theoretical
calc vs. a real world fire don't show up in failure data.  There are many
many reasons for this. Including some fudge in the HW many times, some fudge
in the C factors(more so on newer systems), k factors, density actually
required, and density actually delivered especially on the first couple
heads that open. 

If the hazard and design density are in sync and the valve is open and
something caused the City supply to drop 5 psi and the original RA was 0
safety and the fire starts in the RA does anyone really think the building
is going to burn down?  I don't.  I also don't design like that, it is one
link in the failure chain I can control. 