Our supt recently stopped in to look at a retail store for pricing up
dropping heads. Our competitor stopped in to do the inspection while he was
there. They chatted for 20 minutes, then the guy left. He never went back to
the riser to do his drain test or ring the bell.

When Bill went back to the riser to jot down the particulars, the residual
on the main drain test was 12 PSI. This is a single story 40k SF +/- strip
center, stock area heads likely 17' AFF, or 5 SPI elev difference from the
residual gauge at 5' AFF. So there's enough water pressure to push the first
cap or two off, not much else.

Think the guy who doesn't even walk back to the riser notes the dramatically
low pressure?

There's a 750,000 sf mall across the street. Hope they have a fire pump for
that part.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, December 02, 2009 7:17 AM
To: [email protected]
Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

"We DO maintain annual pressure records in each sprinkler room- hanging on
the main drain tag. Naturally this data is only of value when someone
opening that main drain and writing down the residual pressure actually
compares the result with the previous data."

George, Interestingly I submitted a proposal to NJ DCA C&S to include this
information on the hydraulic data plate, information that's supposed to
obtained at acceptance based on the water supply at the time of
installation, information that sets the baseline. The proposal was shot down
because the committee didn't think it belonged there yet didn't amend the
proposal to require it be posted elsewhere and not just on a report that
gets stuffed in a drawer. Go figure.

The main drain test, while admittedly not absolute, does provide insight as
to water supply degradation. Case in point a local church where a diligent
inspector noted low residual pressure, around 12 psi. Having performed many
drain tests in town before he knew this was unusual and sounded the alert.
Turned out that the fire service main had partially collapsed. The main was
promptly replaced and residual pressures returned to normal. 

This was case of gross declination but what of those whose pressures decline
incrementally ?. There is a need for this baseline information to be posted
at the BOR, preferably on the data plate. Keep in mind we must compare
against the baseline information and not make the mistake of compounding
acceptable loss based on a previous years values. 

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, December 02, 2009 5:21 AM
To: [email protected]
Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

We DO maintain annual pressure records in each sprinkler room- hanging on
the main drain tag. Naturally this data is only of value when someone
opening that main drain and writing down the residual pressure actually
compares the result with the previous data.

You're spot on that the language on future impact is unenforceable and the
discussion of defending your analysis in court- well, where ARE the
guidelines we should apply? Crystal Ball?

Tank gradient adjustment is the tip of a long-ignored iceburg.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Tuesday, December 01, 2009 6:52 PM
To: [email protected]
Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

Steve, your list of design basis considerations do not appear in NFPA 13 or
13R.  Do you think there is a need to address this topic for a future
edition of these documents?  Does AFSA have a task force that can work up a
set of recommendations?

In my opinion, the water supply requirements are so vague as to be
unenforceable and could vary significantly from jurisdiction to
jurisdiction.  How far into the future should we look to determine demand as
is required by NFPA 13?  I normally look to the plumbing/mechanical engineer
for building usage data, but just how deeply do we need to go into a city's
water supply master plan to assess "future demand"?  Do we need to maintain
annual pressure records for each sprinkler system to confirm we don't dip
below our design assumptions?  Should we require a 5-year flow test as part
of an NFPA 25 inspection?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Tuesday, December 01, 2009 4:06 PM
To: [email protected]
Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

I don't disagree with Ron's take, but it may also be prudent to involve
the project civil engineer.  Private mains serving all demands - fire,
domestic, irrigation - can be designed and modeled the same way that
public ones are.   There is a predictable window during each 24 hour
day, sometimes it's as narrow as 15 minutes, other times widened to 60
minutes, known as Peak Day Demand (PDD).   When we request a model from
a water district in lieu of a flow test (a fact of life here in
perpetually drought-stricken SoCal), it is always run with the specified
fire flow added to PDD, which generally already exists in the water
study if they have one.    So ...   contact the project civil engineer
and ask what they used as a basis for their design.   If they have
established a PDD, you can accurately model the performance of that
private main, and flow test back to the point of connection to THAT
main, and not necessarily the public one.   Be sure that the demands of
plumbing and irrigation meters (and/or sub-meters) accounted for, as
well as backflow losses, etc.   Some will argue that's not a prudent
course of action; our experience has been that it's accurate to a
fractional percentage of error. 

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Tuesday, December 01, 2009 12:24 PM
To: [email protected]
Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)

You have to assume that the single main line is feeding domestic
demand to all buildings when the fire occurs and so the fire demand
for the one building is now added to the domestic demand for all
buildings, plus hose stream. If you're being fed from a loop then
domestic demand for the building in question only.

On Tue, Dec 1, 2009 at 12:20 PM, Eric Tysinger <[email protected]>
wrote:
> I don't think I agree with all buildings on the site needing to be
accounted for. One building I just recently finished had a domestic
demand of 375 gpm, if there were 5 of these building on the site, I
would have to account for 1875 gpm? That alone exceeds the available
flow on many projects I have seen.
>
> Eric Tysinger
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
> Sent: Tuesday, December 01, 2009 3:12 PM
> To: [email protected]
> Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition
(Handbook)
>
> Yes, and if there is one tap to several buildings then domestic demand
fore ALL buildings in the complex needs to be accounted for for EACH
hydraulic calc needed.
>
> On Tue, Dec 1, 2009 at 12:11 PM, Eric Tysinger <[email protected]>
wrote:
>> Good afternoon all..
>>
>> I am looking for clarification on when domestic demand is required to
be account for?
>>
>> Based on section 6.5.5, domestic demand is required when common
domestic/fire lines are used. What exactly is the definition of common?
The commentary in the handbook goes on to reference figure A.6.5.3(9)
which doesn't exist, as an example of a combined arrangement. Should
this A.6.5.3(9) be worded as A.6.5.3(a)? If this is the case what about
figure A.6.5.3(b), in this situation where the fire and domestic are
separate connections, would domestic demand be required?
>>
>> In the situation of a community subdivision where the city main is
tapped once, then the water main runs throughout the project feeding
hydrants, domestic and fire lines, and the same arrangement as figure
A.6.5.3(b) is used, would this require domestic demand to be accounted
for?
>>
>> Thanks,
>> Eric Tysinger CET
>> NICET 108988
>> Designer
>> Wayne Automatic Fire Sprinklers, Inc.
>> 4370 Motorsport Drive
>> Concord, NC 28027
>> p: (704)782-3032
>> f: (704)795-6838
>> C: (239)633-9703
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4652 (20091201) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4652 (20091201) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to