As we all know, a water flow tests automatically picks up the other demands on the system. The problem is when a loop is being installed to feed multiple planned buildings on one site. My first point is that it is the EOR's (ok, the sub- engineer) job to size the site main and to tell the contractor the available water supply to be used. WHEN the contractor accepts the role of defining the water supply for their sprinkler system from a facility loop that is yet to be installed (getting dangerously close to performing the E word and arguable outside the scope of 13R), how can they not include the domestic impact on that loop? The challenge is defining that volume. Why would one take the demand for one building then multiple it by the number of buildings. Sure it SOUNDS logical but it's insane (as shown by Eric's example). Having noticed that as the size of the building increases, the volume for the individual units goes down and for really large buildings there is a huge difference. Wouldn't it seem appropriate to treat all the other building in the entire complex as one big building and define the volume that way?
Roland On Dec 2, 2009, at 5:32 AM, Eric Tysinger wrote: > These are all valid points that can be or maybe should be > considered, however none of these requirements are in any codebooks. > The original question was what exactly is the requirement as stated > by NFPA 13R. It gives diagrams for specific examples of preferred > and acceptable arrangements for water supply connections. It also > uses one of these diagrams to show an example of a shared connection > between a fire and domestic line. > > We did a 52 building, multi-family site a year or so back. The site > was actually planned for 104 buildings. Each building had > approximately 100gpm domestic allowance. So what I am gathering for > these posts is that I should have accounted for 104000 gpm? Even at > the number of buildings we actually did it would have been 5200gpm. > I'm sorry but this really sounds way off and definitely not covered > by 13R. > > Thanks, > Eric Tysinger CET _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)