We DO maintain annual pressure records in each sprinkler room- hanging on the main drain tag. Naturally this data is only of value when someone opening that main drain and writing down the residual pressure actually compares the result with the previous data.
You're spot on that the language on future impact is unenforceable and the discussion of defending your analysis in court- well, where ARE the guidelines we should apply? Crystal Ball? Tank gradient adjustment is the tip of a long-ignored iceburg. glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bill Brooks Sent: Tuesday, December 01, 2009 6:52 PM To: [email protected] Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook) Steve, your list of design basis considerations do not appear in NFPA 13 or 13R. Do you think there is a need to address this topic for a future edition of these documents? Does AFSA have a task force that can work up a set of recommendations? In my opinion, the water supply requirements are so vague as to be unenforceable and could vary significantly from jurisdiction to jurisdiction. How far into the future should we look to determine demand as is required by NFPA 13? I normally look to the plumbing/mechanical engineer for building usage data, but just how deeply do we need to go into a city's water supply master plan to assess "future demand"? Do we need to maintain annual pressure records for each sprinkler system to confirm we don't dip below our design assumptions? Should we require a 5-year flow test as part of an NFPA 25 inspection? Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Tuesday, December 01, 2009 4:06 PM To: [email protected] Subject: RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook) I don't disagree with Ron's take, but it may also be prudent to involve the project civil engineer. Private mains serving all demands - fire, domestic, irrigation - can be designed and modeled the same way that public ones are. There is a predictable window during each 24 hour day, sometimes it's as narrow as 15 minutes, other times widened to 60 minutes, known as Peak Day Demand (PDD). When we request a model from a water district in lieu of a flow test (a fact of life here in perpetually drought-stricken SoCal), it is always run with the specified fire flow added to PDD, which generally already exists in the water study if they have one. So ... contact the project civil engineer and ask what they used as a basis for their design. If they have established a PDD, you can accurately model the performance of that private main, and flow test back to the point of connection to THAT main, and not necessarily the public one. Be sure that the demands of plumbing and irrigation meters (and/or sub-meters) accounted for, as well as backflow losses, etc. Some will argue that's not a prudent course of action; our experience has been that it's accurate to a fractional percentage of error. Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Tuesday, December 01, 2009 12:24 PM To: [email protected] Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook) You have to assume that the single main line is feeding domestic demand to all buildings when the fire occurs and so the fire demand for the one building is now added to the domestic demand for all buildings, plus hose stream. If you're being fed from a loop then domestic demand for the building in question only. On Tue, Dec 1, 2009 at 12:20 PM, Eric Tysinger <[email protected]> wrote: > I don't think I agree with all buildings on the site needing to be accounted for. One building I just recently finished had a domestic demand of 375 gpm, if there were 5 of these building on the site, I would have to account for 1875 gpm? That alone exceeds the available flow on many projects I have seen. > > Eric Tysinger > > -----Original Message----- > From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman > Sent: Tuesday, December 01, 2009 3:12 PM > To: [email protected] > Subject: Re: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook) > > Yes, and if there is one tap to several buildings then domestic demand fore ALL buildings in the complex needs to be accounted for for EACH hydraulic calc needed. > > On Tue, Dec 1, 2009 at 12:11 PM, Eric Tysinger <[email protected]> wrote: >> Good afternoon all.. >> >> I am looking for clarification on when domestic demand is required to be account for? >> >> Based on section 6.5.5, domestic demand is required when common domestic/fire lines are used. What exactly is the definition of common? The commentary in the handbook goes on to reference figure A.6.5.3(9) which doesn't exist, as an example of a combined arrangement. Should this A.6.5.3(9) be worded as A.6.5.3(a)? If this is the case what about figure A.6.5.3(b), in this situation where the fire and domestic are separate connections, would domestic demand be required? >> >> In the situation of a community subdivision where the city main is tapped once, then the water main runs throughout the project feeding hydrants, domestic and fire lines, and the same arrangement as figure A.6.5.3(b) is used, would this require domestic demand to be accounted for? >> >> Thanks, >> Eric Tysinger CET >> NICET 108988 >> Designer >> Wayne Automatic Fire Sprinklers, Inc. >> 4370 Motorsport Drive >> Concord, NC 28027 >> p: (704)782-3032 >> f: (704)795-6838 >> C: (239)633-9703 >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email >> to:[email protected] >> (Put the word unsubscribe in the subject field) >> > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering > Bates Technical College > Tacoma, WA > > Member: > SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4652 (20091201) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4652 (20091201) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)