The issue with flowing more than required is not an issue as long as you
don't exceed the velocity of the listing on the device. Exceed that in your
forward flow test and some lawyer will make it look like you intentionally
sabotaged the entire life safety system of the building including the alarm
system. (Besides that fact you probably broke something, that will have to
be replaced.)

Additionally some installation instructions say things like "Minimum 20 PSI
supply pressure recommended"
What happens when you draw it down below 20, cause your overflowing the
device? You've violated the installation instructions, or so the lawyer
says.

Overflowing has consequences.

Thom McMahon, SET
Firetech, Inc.