The backflow should be sized for its design flow at 15 fps per it's listing.
Conversely, I've seen them oversized, or 'pipe sized', just like PRV's.
TD


That brings up another point I have noticed, mostly by U/G contractors. They
place a smaller backflow inline, and then come back to pipe size. In other
words, 6" piping, 4" backflow, and then back to 6". I know it is done to
save $$$. But there is no code reference to say you can't. I found the
answer in the listing. A 4" for example has a rated working gpm of 500. It
is UL tested to 750gpm. If your system demand exceeds the "maxed out" gpm of
the device, what impact will there be on the backflow attempting to flow
these demands in subsequent years?

R/
Matt 

 