We have a customer whose pre-action system for a library is impaired due to 
electrical/ detection
problems. He has had a contractor trip it into a wet pipe system. We are 
looking for a code reference
prohibiting this kind of "repair". Is this possibly just an AHJ decision?
Any suggestions?

C. Burton Ford
Designer- NICET Certified: Fire Alarm, 
Special Hazards, Sprinkler Design 
&Sprinkler Inspections
NFPA CFPS
Cintas Fire Protection-D-47
Warminster, PA 18974
Phone 267-487-1000
Fax 267-487-1010

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On
Behalf Of Richardson, R
Sent: Friday, February 12, 2010 10:37 AM
To: [email protected]
Subject: RE: Flexible Pipe

The engineer quite likely means the use of high pressure steel braided rubber 
hose, or something
similar.

We have approved high pressure steel braided rubber hose for these situations 
often, as long as they
installation is such that the hose remain submerged.  Not a whole lot of better 
options that we are
aware of at this point.

Rich Richardson
Seattle Fire Department

>
> Yeah you read this right.
>
> I'm reviewing a pacakge and the EOR has called out for flexible pipe at a
> couple of areas where he thinks they can't use hard pipe to make the bends,
> plus he is wanting some allowance for movement.  This is on a pier.
>
> So I've hunted even though in all my years dabbling in this I can't recall
> such an animal.  Flexible connections and flexible drops are one thing but a
> 10-20 ft section of "flexible" pipe?
>
> Anyone ever heard or seen such a thing?
>
> He's not called out any manufacturer and is out of town right now so I can't
> ask what he had in mind.
>
> It's not a sprinkler system,  it's a 4" manual, dry standpipe line along the
> pier.
>
>
> CH2MHILL/SPB
> Craig Prahl
> 864-599-4102
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman, CET, FPE
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.  Your assistance in correcting this 
error is appreciated.  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)