Yup=-
And just plug it with a mech tee when repairs to the detection system are
completed.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Vining
Sent: Friday, February 12, 2010 11:27 AM
To: [email protected]
Subject: Re: Impaired preaction

How will they get an alarm if a sprinkler operates.  They could install a
waterflow indicator, but it would have to be removed if they ever use the
preaction valve again.

Ed Vining

On Fri, Feb 12, 2010 at 8:01 AM, Steve Leyton
<[email protected]>wrote:

> If it's a library, unless portions of the system are inappropriately
> exposed to sub-40 deg. temps, there isn't a code requirement that a
> library be protected by a particular KIND of system, just that it be per
> the referenced standard (13).    Which gives the designer a choice, that
> was likely exercised to mitigate the chance of a false discharge
> irreparably damaging books, archival collections, etc.   And likely
> specified that way.   I doubt you'll find a code violation, but the
> first cost of preaction was undertaken for a reason, so it's the
> library's decision to put it back into preaction service or not.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ford,
> Charles
> Sent: Friday, February 12, 2010 7:55 AM
> To: [email protected]
> Subject: RE: Impaired preaction
>
> We have a customer whose pre-action system for a library is impaired due
> to electrical/ detection
> problems. He has had a contractor trip it into a wet pipe system. We are
> looking for a code reference
> prohibiting this kind of "repair". Is this possibly just an AHJ
> decision?
> Any suggestions?
>
> C. Burton Ford
> Designer- NICET Certified: Fire Alarm,
> Special Hazards, Sprinkler Design
> &Sprinkler Inspections
> NFPA CFPS
> Cintas Fire Protection-D-47
> Warminster, PA 18974
> Phone 267-487-1000
> Fax 267-487-1010
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On
> Behalf Of Richardson, R
> Sent: Friday, February 12, 2010 10:37 AM
> To: [email protected]
> Subject: RE: Flexible Pipe
>
> The engineer quite likely means the use of high pressure steel braided
> rubber hose, or something
> similar.
>
> We have approved high pressure steel braided rubber hose for these
> situations often, as long as they
> installation is such that the hose remain submerged.  Not a whole lot of
> better options that we are
> aware of at this point.
>
> Rich Richardson
> Seattle Fire Department
>
> >
> > Yeah you read this right.
> >
> > I'm reviewing a pacakge and the EOR has called out for flexible pipe
> at a
> > couple of areas where he thinks they can't use hard pipe to make the
> bends,
> > plus he is wanting some allowance for movement.  This is on a pier.
> >
> > So I've hunted even though in all my years dabbling in this I can't
> recall
> > such an animal.  Flexible connections and flexible drops are one thing
> but a
> > 10-20 ft section of "flexible" pipe?
> >
> > Anyone ever heard or seen such a thing?
> >
> > He's not called out any manufacturer and is out of town right now so I
> can't
> > ask what he had in mind.
> >
> > It's not a sprinkler system,  it's a 4" manual, dry standpipe line
> along the
> > pier.
> >
> >
> > CH2MHILL/SPB
> > Craig Prahl
> > 864-599-4102
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
>
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
>
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman, CET, FPE
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
>
>
> This e-mail transmission contains information that is intended to be
> confidential and privileged.  If you receive this e-mail and you are not
> a named addressee you are hereby notified that you are not authorized to
> read, print, retain, copy or disseminate this communication without the
> consent of the sender and that doing so is prohibited and may be
> unlawful.  Please reply to the message immediately by informing the
> sender that the message was misdirected.  After replying, please delete
> and otherwise erase it and any attachments from your computer system.
> Your assistance in correcting this error is appreciated.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
>
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4861 (20100212) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4861 (20100212) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to