If it's the same distance from the head, and still 2'-6" down from the
ceiling, the depth of the soffit doesn't matter, the water still hits it,
and falls to the floor without wetting the wall.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Friday, February 26, 2010 2:39 PM
To: [email protected]
Subject: RE: sidewall obstruction

What if the soffit was 6" deep (wall to edge of soffit)?

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: February 26, 2010 2:25 PM
To: [email protected]
Subject: RE: sidewall obstruction

Ok let's see if I can articulate this so it's understandable.
My understanding of the spray pattern for Residential sprinkler heads is
that they supply the majority of the water to the wall surfaces(Wall
Wetting) less than 36" down from the ceiling. When you have a soffit that is
2'-6" down from the ceiling, it's very hard for that sprinkler head to wet
the wall below that soffit. The majority of the water will hit the soffit,
and drop to the floor, without wetting the rest of the wall. The depth of
the soffit, from the wall to the edge of the soffit, is not the important
thing, it is the distance from the head to the soffit that makes it able to
spray under the soffit and wet the wall or not. Deeper soffits must be
farther away from the head for water to get to the wall below the soffit.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Friday, February 26, 2010 1:48 PM
To: [email protected]
Subject: RE: sidewall obstruction

Okay, now if the bulkhead is only 6" wide (instead of 2'-6") and the near
edge of the bulkhead is still 9' away from the s/w head, is it still an
obstruction? 


When I asked these questions from Tyco, they referred me to the table and
said it was an obstruction.

Tony   

d)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)