I had one of these in a Mercedes Benz dealership in 2002ish and it was almost 
two stories tall by 10 foot wide and about 4 foot deep.

The AHJ had us put in concealed heads (200 deg) in the front corners, it gave 
the greatest vertical access since the motor, belts, and structure were located 
on the sides.  Concealed and corners also eliminated mechanical damage from the 
rotating bins.  It was also before the 8.1.1 (7) exception for furniture like 
items not intended for occupancy.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, February 26, 2010 8:24 AM
To: [email protected]
Subject: Carousel Storage Units

I've been searching NFPA 13 for info on protection of these type of storage 
units.   They are typically fully enclosed, have rows of plastic bins which are 
linked together by a drive mechanism, often computer indexed to an operator can 
enter a part number and the rows of bins rotate until the appropriate row is at 
the operator opening for access.  They can be of any size, we're looking at 
about 10-15 feet wide, about 5-10 ft deep and about 20 ft tall.  The parts in 
the plastic bins are supposed to be mostly non-combustible (they used the term 
mostly and that's all they'll share).

http://www.kardexremstar.com/content/products/vertical/

I can't find anything in 13, so either the Standard doesn't address these or 
I'm using the wrong term.

I do know there is an FM Data Sheet on them but we are directed not to follow 
FM data.  This is a foreign client who insists that if it's not in the Building 
or Fire code they are not going to do it regardless of who says to do what.  I 
can't argue with that but I do need to make sure the situation has been 
addressed.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

--
ExchangeDefender Message Security: Click below to verify authenticity
http://www.exchangedefender.com/verify.asp?id=o1QH3o85031823&[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to