Ok let's see if I can articulate this so it's understandable. My understanding of the spray pattern for Residential sprinkler heads is that they supply the majority of the water to the wall surfaces(Wall Wetting) less than 36" down from the ceiling. When you have a soffit that is 2'-6" down from the ceiling, it's very hard for that sprinkler head to wet the wall below that soffit. The majority of the water will hit the soffit, and drop to the floor, without wetting the rest of the wall. The depth of the soffit, from the wall to the edge of the soffit, is not the important thing, it is the distance from the head to the soffit that makes it able to spray under the soffit and wet the wall or not. Deeper soffits must be farther away from the head for water to get to the wall below the soffit.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of A.P.Silva Sent: Friday, February 26, 2010 1:48 PM To: [email protected] Subject: RE: sidewall obstruction Okay, now if the bulkhead is only 6" wide (instead of 2'-6") and the near edge of the bulkhead is still 9' away from the s/w head, is it still an obstruction? When I asked these questions from Tyco, they referred me to the table and said it was an obstruction. Tony d) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)